Central Air filter housing

I have a ceiling mounted filter for my central air system. The filter is a metal lifetime electrostatic type. I have never tried a standard throwaway filter.

Problem is that the recess for the filter is at least 2" deep with the grate closed and the filter is resting on the grate. I put in some weather stripping in the filter seat area but it still floats in the recess. The filter gets sucked up when the fan turns on. Is this happening because the lifetime filter is heavier?

Thanks
 
Sponsored Links
  #2  
Old 01-27-05, 08:13 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
YEs, the electrstic filters are heavier in a way.. Put some cardboard in to wedge the filter in place so it's not going up and down on you.

Throw away the eletrostic filter, they don't work well over time, and really cuts down on the air flow as well.
 
  #3  
Old 01-29-05, 03:00 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
Wink

Me to::::: Dont use that kind of filter for sure get a good plated one. You say the filter frame is made for a 2" filter. So like we used to do all the time. Get two filters now and put them in Dont go over a MERV 5 on them. Now when comes time to change them just throw the out side one away. Put the new filter in first then that older on top of it so air goes in it first. This work very good.

ED
 
  #4  
Old 01-29-05, 03:40 PM
scottg's Avatar
Member
Join Date: Dec 2004
Location: Wilmington, NC hurricane magnet of the U.S.A.
Posts: 259
Received 0 Votes on 0 Posts
What is the filter size?
What is the air conditioner size?
You need to have at least bare minimum 200 sq. in. per ton
Mind you that is minimum.
So if you have a 2 ton A/C or 24k BTU than a 20X20 filter is the minimum size to go with.
The minimum size has always also told me minimum grade.
Better grade filters need to be larger than minimum size.
For a merv 5 or lower add 20% to the size
Than that 20x20 becomes a 20x25.
If this is not done then you will not get the correct amount of air through for tha A/C to run and then you could have compressor failures.
 
  #5  
Old 01-31-05, 05:32 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,247
Received 23 Votes on 21 Posts
If possibe, I suggest the 4-5" thick pleated filters. Due to the large surface area, they can provide very good filtration with low air restriction.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: