Need advice for bathroom exhaust fan upgrade.

Reply

  #1  
Old 08-18-06, 01:22 AM
Z
Member
Thread Starter
Join Date: Aug 2006
Posts: 2
Received 0 Votes on 0 Posts
Question Need advice for bathroom exhaust fan upgrade.

We currently have a Broan 50 CFM fan in our 100 sq ft. ensuite bathroom.
The 50 CFM is not enough for a bathroom of our size and we want to upgrade to a 110 CFM unit.

The current 50 CFM uses a 3" duct which runs through the attic to a 3" roof cap.
The new 110 CFM exhaust fan requires a 4" duct.

My question is, can I run a new 4" duct up to the existing 3" roof cap and connect the two using a 4" to 3" adapter?

The Nutone instructions say "no" as it will impede the flow and cause excess noise.

Normally I would follow the instructions but I have no way of getting on the roof (30+ feet and steep) and a contractor quoted me $500 to switch out the roof cap.

Thanks,
Zak
 
  #2  
Old 08-18-06, 05:32 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
Yes, you may use the 4-to-3 reducer at the roof jack. It is not the prefered method, it will add some back pressure which will cause increased noise and decreased performance but it will still be far, far better than simply exhausting into the attic.

Try to find a tapered reducer as opposed to a concentric reducer. The concentric reducer is more likely to creat eddy currents that will further impede the air flow.

I don't know what kind of a "contractor" you asked but I would ask a roofer. If there are any re-roof jobs being done in your area you might ask the job foreman if he or any of his crew is interested in a small "side" job. I'm pretty darn sure that you could get the proper roof jack installed for far less than $500.
 
  #3  
Old 10-17-06, 12:04 PM
S
Member
Join Date: Oct 2006
Posts: 2
Received 0 Votes on 0 Posts
I have been researching this because I must go from 4" to 6". The prior answer is right. Trouble is, you will not get the full output because of static pressure, and will get some noise. You can reduce the noise by using an insulated duct. But most noise is a function of the fan itself.

But it's also right that there is no way replacing one roof vent with another, without other work, costs $500. It takes a few minutes for a skilled person.
 
  #4  
Old 10-17-06, 09:39 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
Wink

It also help some to make the tapered reducer
longer. Any sheet metal shop or hvac can make you one up.

ED
 
 