Converting from natural gas to propane

I have a sears 2 sided wall furnace that i am trying to get converted over to propane. The burners and pilot have been converted but when the furnace kicks off the propane still comes out there for the burners never shut off. Do i need a stronger spring in the electrical control module to press harder on the seal to shut it off? Need help, its getting cold!!!!!!
 
Sponsored Links
  #2  
Old 11-22-08, 02:43 PM
S
Member
Join Date: Sep 2008
Location: Long Island
Posts: 769
Received 0 Votes on 0 Posts
"kicking off" you mean the stat satisfies there?call the heat in again with the stat,and then go to the gas valve and pull 1 wire off to see if it closes off 100%...if not you need a valve update.thank god you have a standing pilot weeeee hope!
 
  #3  
Old 11-23-08, 11:39 AM
A
Member
Thread Starter
Join Date: Nov 2008
Location: Oklahoma
Posts: 2
Received 0 Votes on 0 Posts
What exactly is a valve update? What all does it involve?
 
  #4  
Old 11-23-08, 12:47 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,231
Received 22 Votes on 20 Posts
Natural to LP

In addition to changing the orifices, the gas valve also needs to be converted or changed. Some gas valves are convertable, some are not.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: