static pressure

I have a goodman 2.5 ton. I am trying to figure out the external static pressure. Goodman says it should be .2. I acquired a manometer. I hooked up two probes one to the return between the air filter and the a coil. The other to the supply side in the plenum above the a coil. The combined reading I get is .4 with air filter in and .2 with it out. Is this ok or do I need to enlarge the register opening. This is with a brand new filter
 
  #2  
Old 08-12-15, 04:40 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
That sounds about right. What kind of filter?
 
  #3  
Old 08-12-15, 11:58 AM
F
Member
Thread Starter
Join Date: Aug 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks. Cheapest filter lowes had.
 
  #4  
Old 08-13-15, 04:52 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
If your having issues id make sure the duct is sized correctly. Sized correctly duct on residential is very rare.
 
 