Wiring Tjernlund Airshare
#1
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Wiring Tjernlund Airshare
I have an Aprilaire 360 whole house humidifier wires to a nest thermostat. Everything works as expected.
I have a Tjernlumd AS2 that moves air through a wall in my house to an adjoining room. I’m wondering if there is a way to wire the 24v connections so that the airshare operates with fan of the humidifier?
wiring diagram can be found here: https://tjernlund.com/Tjernlund_FC24...er_8504210.pdf
I have a Tjernlumd AS2 that moves air through a wall in my house to an adjoining room. I’m wondering if there is a way to wire the 24v connections so that the airshare operates with fan of the humidifier?
wiring diagram can be found here: https://tjernlund.com/Tjernlund_FC24...er_8504210.pdf
#2
Follow the modified diagram. You won't be using the 24vac transformer on the FC-24. You will need to connect the identified yellow and violet wires to the same place the humidifier solenoid connects.

Last edited by PJmax; 02-17-18 at 08:40 PM. Reason: updated diagram for timer
#3
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Hi, Pete!
I got this all wired up today, but I need some troubleshooting.
I wired as you indicated, but the Aireshare fan runs continuously. I'm trying to get it so that it only runs when the humidifier turns on and off.
I have the Aireshare yellow and violet wires connected to the same relay terminals as the humidifier solenoid wires.
I got this all wired up today, but I need some troubleshooting.
I wired as you indicated, but the Aireshare fan runs continuously. I'm trying to get it so that it only runs when the humidifier turns on and off.
I have the Aireshare yellow and violet wires connected to the same relay terminals as the humidifier solenoid wires.
#4
Does the solenoid remain energized too ?
The 360 may be a power humidifier. Can you remove the external wiring to it and just try shorting the two solenoid wires together. Does that energize the solenoid ?
The 360 may be a power humidifier. Can you remove the external wiring to it and just try shorting the two solenoid wires together. Does that energize the solenoid ?
#7
Ok.... disconnect the aireshare unit.
Do you have a relay connecting the 360 to the nest..... you should ?
Do you have a relay connecting the 360 to the nest..... you should ?
#13
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Hey, Pete. On a similar note, is it possible to do the same thing with the Tjernlund ASLL (through the floor unit)? Is there a way to wire it to the same relay?
https://tjernlund.com/Tjernlund_ASLL...%208504156.pdf
https://tjernlund.com/Tjernlund_ASLL...%208504156.pdf
#14
That unit has no internal switching relay.
In order to have the nest control it.... it will need its own relay.
In order to have the nest control it.... it will need its own relay.
#15
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Thanks again for your help, Pete. The Aireshare works as it should with the humidifier.
Now to add some complexity, I have another question. Given the wiring you suggested, is there a way to modify the setup so that the Airshare can run for 10 extra minutes after the humidifier shuts off? Is it possible to link in something like this timer relay?
https://www.tjernlund.com/Tjernlund_950-1067.pdf
Now to add some complexity, I have another question. Given the wiring you suggested, is there a way to modify the setup so that the Airshare can run for 10 extra minutes after the humidifier shuts off? Is it possible to link in something like this timer relay?
https://www.tjernlund.com/Tjernlund_950-1067.pdf
#16
Ok.... I added the timer module into the original diagram in post 2.
The module input gets connected to the same 24vac as the relay. No polarity.
The three numbers in red refer to the timer terminals.
The module input gets connected to the same 24vac as the relay. No polarity.
The three numbers in red refer to the timer terminals.
#18
The FC24 keeps the fan running when there is 24vac present.
The timer only runs the fan for a short (delayed time).
So both need to be used together.
Hmmmmm..... does the timer keep the fan on and when the 24vac gets removed... the countdown starts. That is the question.
I don't know 100% if the timer can replace the FC-24. It may be able because it's a post purge timer. Holds closed when powered and for XX minutes after power is removed..
The timer only runs the fan for a short (delayed time).
So both need to be used together.
Hmmmmm..... does the timer keep the fan on and when the 24vac gets removed... the countdown starts. That is the question.
I don't know 100% if the timer can replace the FC-24. It may be able because it's a post purge timer. Holds closed when powered and for XX minutes after power is removed..
#22
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
So now I have a humidifier hooked up in my finished basement. It is wired to a nest thermostat on the first floor by way of a relay between the boiler and the humidifier. I also have the AS2 Aireshare wired to this setup, so the Aireshare comes on with the humidifier to draw air up to the first floor. It works well. And the timer relay on the Aireshare runs the unit for 10 additional minutes once the humidifier shuts off as determined by the Nest
Now for the the next phase: I would like to put an Aireshare ASLL through-the-floor unit on the opposite end of the basement to operate the same way as the AS2. Besides running 120v to the ASLL, I imagine I will need at least a 120/24 transformer and another timer relay. I can’t really wrap my head around how to make all of the necessary connections. I’m wondering if this is something you could brainstorm for me?
https://tjernlund.com/Tjernlund_ASLL...%208504156.pdf
Now for the the next phase: I would like to put an Aireshare ASLL through-the-floor unit on the opposite end of the basement to operate the same way as the AS2. Besides running 120v to the ASLL, I imagine I will need at least a 120/24 transformer and another timer relay. I can’t really wrap my head around how to make all of the necessary connections. I’m wondering if this is something you could brainstorm for me?
https://tjernlund.com/Tjernlund_ASLL...%208504156.pdf
#23
You could just run a piece of 14-2 w/ground NM-b (romex) cable from the working unit to the new one. This cable would bring switched 120v to the the new unit.
#25
Not sure what you are asking.
The romex connects at the timer module and then at the new new unit. You can't just have connections in midair so it does need to go to some type of box.
The romex connects at the timer module and then at the new new unit. You can't just have connections in midair so it does need to go to some type of box.
#26
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Sorry. To be more clear:
I have access to the romex line right right next to where I will install the new ASLL. Can I put in a work box and splice in a branch to the ASLL?
Or, as I think you are saying, I need to connect to the pigtails where the timer relay is installed.
I have access to the romex line right right next to where I will install the new ASLL. Can I put in a work box and splice in a branch to the ASLL?
Or, as I think you are saying, I need to connect to the pigtails where the timer relay is installed.
#27
You need to get power from the first unit. Where the timer is installed. A timer module can only switch one circuit so you can't connect to any existing live romex cable.
Your second unit will connect to N, splice 1 and ground as based on the diagram in post 2.
Your second unit will connect to N, splice 1 and ground as based on the diagram in post 2.
#29
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
And, finally, not even sure this is possible:
During the summer months, I run a dehumidifier in the finished basement. In the winter months, it's not necessary; however, there are some days like today when it's warm outside and the basement humidity goes up to 50-55% (about 10% higher than the first floor).
Is there a way to wire the basement Nest to the same AS2 and ASLL fans, so that they would turn on when the basement humidity went above 50%? Just shooting for the moon here ...!
During the summer months, I run a dehumidifier in the finished basement. In the winter months, it's not necessary; however, there are some days like today when it's warm outside and the basement humidity goes up to 50-55% (about 10% higher than the first floor).
Is there a way to wire the basement Nest to the same AS2 and ASLL fans, so that they would turn on when the basement humidity went above 50%? Just shooting for the moon here ...!
#30
You mean use the upstairs nest for humidifying and the downstairs nest for dehumidifying ?
You can't have the two nests tied together. You would have to switch wiring from one to the other.
You can't have the two nests tied together. You would have to switch wiring from one to the other.
#31
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Yup, that’s what I meant, but I understand what you are saying.
Instead of linking both Aireshares together, what if I used the basement Nest to run the second fan for dehumidify? Is that possible in heating mode? And are we back to needing a 120/24 transformer and a relay?
Instead of linking both Aireshares together, what if I used the basement Nest to run the second fan for dehumidify? Is that possible in heating mode? And are we back to needing a 120/24 transformer and a relay?
#32
Member
Thread Starter
Join Date: Jan 2018
Posts: 53
Received 0 Votes
on
0 Posts
Talked with Nest support today. They say the basement Nest can be used to run a fan to dehumidify while in heating mode. Understandably, they wouldn't give me more specifics though because I'm not a Nest Pro.