How to interpret air flow charts

I'm looking at air flow charts for a Mitsubishi mini-split ducted/concealed indoor unit. Specifically SEZ-KD18NA4. I totally get how an individual charts shows CFM vs external static pressure for each of the 3 fan speeds. What I'm not understanding at all is why there are 4 charts. Each chart is labeled with a different external static pressure, but that's also varied on the vertical axis. Does anyone know what the 4 charts represent or what I'm missing? (Their other ducted units have similar multiple-charts.)
 
Attached Images  
  #2  
Old 07-08-18, 05:48 AM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,500
Received 68 Upvotes on 62 Posts
Ezee question!

Static pressure increases in proportion to airflow.
More airflow = higher static pressure.
 
  #3  
Old 07-08-18, 11:10 AM
T
Member
Thread Starter
Join Date: Jul 2018
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the tip, I had not understood that each of the charts corresponds to a design point / rated point.
 
 