Whistling sound from new A/C zone damper

We had a brand new AC (2 stage) and 2 zone Thermostat with mechanical dampers installed because our upstairs was way hotter than the lower levels (duh). Two ducts supply the basement/main level and one duct supplies the upstairs.

Whenever the upstairs is cooling, we can hear an [annoying] whistling sound coming through the lower levels' vents (as a result of those dampers being closed - my guess).

Questions:
1. How can I reduce/remove the whistling sound coming from the lower levels?
2. Is there an ideal level to set the cfm or pressure on the dampers?

Thank you!
 
Sponsored Links
  #2  
Old 07-25-18, 01:34 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,795
Received 8 Votes on 8 Posts
Zoned systems are very complicated. Sounds like the duct is the wrong size are bypass is not working. Best to call the company back and let them fix it.
 
  #3  
Old 07-25-18, 03:03 PM
T
Member
Thread Starter
Join Date: Jul 2018
Posts: 3
Received 0 Votes on 0 Posts
I agree entirely. The company is coming out tomorrow. I just wanted to educate myself to keep them honest. The individual I spoke to mentioned something about adjusting the cfm. I don't have anything to base my feeling off of, but that doesn't feel like the right solution. Thanks for your reply!
 
  #4  
Old 07-25-18, 04:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,772
Received 1,193 Votes on 1,104 Posts
The CFM for the entire system can't just be lowered. The entire system requires a certain CFM. One duct may only require half. There may be a way of adjusting the blower speed electronically. If not then a certain amount of air needs to be bypassed to keep the system from howling or whistling.

Adding multi zone control to an already installed duct work system is a comprise. When I've had to service an existing system with a problem similar to yours..... I wouldn't allow the primary damper (first floor) to fully close..... allowing some air flow to the system.
 
  #5  
Old 07-31-18, 07:09 AM
T
Member
Thread Starter
Join Date: Jul 2018
Posts: 3
Received 0 Votes on 0 Posts
There appears to be resolution....

The company came out and after troubleshooting and weighing options, lowered the CFM based on the number of registers and the size of the unit (there is an equation for an acceptable range). The diluted explanation is that too much air was being pumped to satisfy the up-stairs/zone 2 which caused whistling to be heard down-stairs/zone 1.

Without compromising time to comfort and without decreasing efficiency, the CFM was decreased to 900. (Zone 1 was at 1200 and zone 2 was at 1100) (The effective range for the unit for the size is 1800).

I will be keeping an eye on the energy usage as well as the comfort level.
 
  #6  
Old 07-31-18, 08:30 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,772
Received 1,193 Votes on 1,104 Posts
Stop back and let us know how it's working. In my opinion..... the system CFM may be too low now.
The ultimate solution is having it set up for two speeds based on one or two dampers open.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: