wiring


  #1  
Old 07-31-02, 02:06 PM
rdmd3
Visiting Guest
Posts: n/a
Arrow wiring

I want to put in a breaker in my main breaker box and run a line to a 30ft travel trailer. I am not sure of the size of the breaker to add and the size of the line. The trailer is about 60ft away from my house. The box in the trailer says to use a 30a breaker. I have 200 amp service to the main box.
 
  #2  
Old 07-31-02, 04:01 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes,, number 10 wire and a 30 A breaker.
 
  #3  
Old 07-31-02, 04:03 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also this is a single pole breaker and is 110 volt. You can get a recept to match your trailer at the trailer place.
 
  #4  
Old 07-31-02, 04:04 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Maybe I should say 120 volt.
 
  #5  
Old 07-31-02, 04:29 PM
rdmd3
Visiting Guest
Posts: n/a
I can connect the 30 amp breaker in my main breaker box?
 
  #6  
Old 07-31-02, 04:31 PM
rdmd3
Visiting Guest
Posts: n/a
there is a 40 amp breaker in the box allready that isn't being used. It was for my electric stove before we changed to gas, can I use that breaker instead of a 30, or is it to much?
 
  #7  
Old 07-31-02, 06:35 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
No, don't use the 40. Get a 30.
 
  #8  
Old 07-31-02, 07:18 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also that 40 is a double pole,,, your travel trailer is single.
 
 