A live in and old house with 2 prong outlets and replaced them with self-grounding 3 prong outlets, but when I test them with a circuit analyzer it says that the ground is open. Did I do something wrong?
 
Sponsored Links
  #2  
Old 09-03-00, 02:47 PM
Visiting Guest
Posts: n/a
Post

Unless you pulled a ground wire from the main box to the outlets, you have no ground and they will test as a open ground.
 
  #3  
Old 09-04-00, 05:29 PM
BoatMech's Avatar
Member
Join Date: Dec 1999
Location: Los angeles
Posts: 592
Upvotes: 0
Received 0 Votes on 0 Posts
Post

IF you installed two prong receptacles with 3 prong receptacles you must install a grounding conductor or protect that circuit with a GFI control protecting all receptacles on that circuit. 210-7-D

Good luck

Wg
 
  #4  
Old 09-05-00, 05:54 AM
Visiting Guest
Posts: n/a
Post

Thanks for the help.
 
  #5  
Old 09-05-00, 07:04 AM
Visiting Guest
Posts: n/a
Post

What the heck is a "self-grounding outlet"? I've never heard of such a thing.
 
  #6  
Old 09-05-00, 07:46 AM
Visiting Guest
Posts: n/a
Post

It's terminology referring to the fact that the outlet will ground itself through the yoke or strap when connected to a properly grounded box.

Pete
 
  #7  
Old 09-05-00, 10:12 PM
BoatMech's Avatar
Member
Join Date: Dec 1999
Location: Los angeles
Posts: 592
Upvotes: 0
Received 0 Votes on 0 Posts
Post

Johnny

Pete is right.

A little more detail. self grounding receptacles are usually found in industrial setting where metal conduit is installed. The metal conduit serves as the grounding conductor. The self grounding receptalce eliminates the requirement of installing a pigtail to from the receptacle to the metal box completing the grounding circuit.
A self grounding receptacle has a little spring loaded clip that ensures constant contact with the steel box that is securely connected to the metal conduit used as the grounding conductor.
Self grounding receptacles sometimes are used in a Romex dwelling situation where the E/C connects the bare wire of the Romex to the steel box and then installs a self grounding receptacle to complete the circuit to the yoke of the receptacle.

Hope this helps

Wg
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: