baseboard heater - wire size


  #1  
Old 08-26-02, 06:26 PM
nigel
Visiting Guest
Posts: n/a
baseboard heater - wire size

I ran 14/2 wire for a baseboard heater in my basement, 1500watts, on 240 volt circuit (I wired to a double pole 15 amp breaker), ...my drywall guy said I should've used 12/2 wire, since the heater is about 75 feet from the panel.

My calculation would show that each wire in the 14/2 is carrying about 6.25 amps, which I figured should be ok to use only 14/2.

Is my drywall guy right? Neither of us are electricians (obviously)!

Thx
 
  #2  
Old 08-26-02, 08:33 PM
A
Master Electrician
Join Date: Dec 2001
Location: Indiana
Posts: 296
Upvotes: 0
Received 0 Upvotes on 0 Posts
calc

If my calc is correct, than this wire has a 2.94% volt drop at this distance with 6.25 load. Your allowed 3%, but its better to have 0%. A 14 conductor 15amp single curcuit is not allowed to exceed 50% of 15 amps(7.25)amps. Your at 6.25 "your ok" both ways.
 
  #3  
Old 08-27-02, 04:36 PM
nigel
Visiting Guest
Posts: n/a
Thanks. You have eased my concerns, and confirmed what I heard from 2 others. The drywall guy should stick to sheet rock I think and stop scaring novice DIY'rs!
 
  #4  
Old 08-27-02, 07:51 PM
M
Member
Join Date: Jan 2002
Location: Illinios
Posts: 242
Upvotes: 0
Received 0 Upvotes on 0 Posts
good thing you have that disclaimer..

Your allowed to load a continous <more than 3 hours> circuit a maxium of 80%......
 
 