baseboard heater - wire size

Reply

  #1  
Old 08-26-02, 06:26 PM
nigel
Visiting Guest
Posts: n/a
baseboard heater - wire size

I ran 14/2 wire for a baseboard heater in my basement, 1500watts, on 240 volt circuit (I wired to a double pole 15 amp breaker), ...my drywall guy said I should've used 12/2 wire, since the heater is about 75 feet from the panel.

My calculation would show that each wire in the 14/2 is carrying about 6.25 amps, which I figured should be ok to use only 14/2.

Is my drywall guy right? Neither of us are electricians (obviously)!

Thx
 
Sponsored Links
  #2  
Old 08-26-02, 08:33 PM
Master Electrician
Join Date: Dec 2001
Location: Indiana
Posts: 300
Received 0 Votes on 0 Posts
calc

If my calc is correct, than this wire has a 2.94% volt drop at this distance with 6.25 load. Your allowed 3%, but its better to have 0%. A 14 conductor 15amp single curcuit is not allowed to exceed 50% of 15 amps(7.25)amps. Your at 6.25 "your ok" both ways.
 
  #3  
Old 08-27-02, 04:36 PM
nigel
Visiting Guest
Posts: n/a
Thanks. You have eased my concerns, and confirmed what I heard from 2 others. The drywall guy should stick to sheet rock I think and stop scaring novice DIY'rs!
 
  #4  
Old 08-27-02, 07:51 PM
Member
Join Date: Jan 2002
Location: Illinios
Posts: 258
Received 0 Votes on 0 Posts
good thing you have that disclaimer..

Your allowed to load a continous <more than 3 hours> circuit a maxium of 80%......
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: