De-Rating Circuits/Breaker

I'm going to run a 10-3 w/ground to my detached garage. Garage is 90 feet from house.

Question: Is a 30amp (2pole) breaker ok or can I go up to 40amp?
 
Sponsored Links
  #2  
Old 08-28-02, 09:04 AM
RickM
Visiting Guest
Posts: n/a
#10 is limited to 30amps maximum.

Rick Miell
 
  #3  
Old 08-28-02, 10:52 AM
Member
Thread Starter
Join Date: Oct 2001
Location: Minneapolis
Posts: 61
Received 0 Votes on 0 Posts
30 amp it is, then

thanks for the reply.
 