Interesting Question.........
#1
#4
Member
Join Date: Dec 2001
Location: Calgary Canada
Posts: 690
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Taking a plug off an item in most cases violates its UL listing which is required by code on manufactured part installed in a system. You would have to check the UL listing for the device and see if it is allowable if it is not then you could still do it if you had an UL inspector check it afterwards. Or in some counties the electrical inspector can make the call although if he does insurances might give you a hassle if anything goes wrong
Most major appliances (stoves, dryers etc) are manufactured and listed to be plugged in or hardwired. so it may be legal under specific conditions
Most major appliances (stoves, dryers etc) are manufactured and listed to be plugged in or hardwired. so it may be legal under specific conditions
#7
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My conception of "hard-wired" is a connection with the branch-circuit conductors terminating at an internal connection point on or inside the load being connected.
#8
Member
Join Date: Dec 2001
Location: Calgary Canada
Posts: 690
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pattbaa is right on the term hard wired. Many models of garage door openers are designed for plug and play but are also allowed to be hard wired by the specifications the manufacturers had them rated at. You can check with UL on the net and see what they have your make and model rated for.