Central AC fan


  #1  
Old 09-10-02, 09:28 PM
GiveMeLight
Visiting Guest
Posts: n/a
Unhappy Central AC fan

The fan (outside the house) on my central ac unit doesn't come on when the flip the switch to ON on my thermostat (inside the house). The blower on the furnace blows fairly cool air for a few minutes, then the air warms up again. Whats going on?
 
  #2  
Old 09-11-02, 04:38 AM
Matt Marsh
Visiting Guest
Posts: n/a
If the fan is not running, it is not removing any heat, therefore the system is tripping out on high head pressure or compressor overload. It would be very difficult to pinpoint the problem positively without actually being there to test and see for myself, but it is likely that the problem is either the fan motor itself is burned out, or bad control relay. But there are also other components in the circuit that could be bad. Do not keep attempting to start the unit until it is repaired, it is very hard on the compressor to overload it.
 
  #3  
Old 09-11-02, 03:54 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes on 0 Posts
Maybe it'd the starting capacitor for the fan motor .Remove the cover for access to the electrical connections and you may fine the schematic inside the cover. Go to an HVAC supply-house with the schematic and all unit info- make,model, serial #, etc. and they will advise you. The capacitor may have "push-on" connections. YOU MUST discharge the old capacitor by shorting across the connection terminals. You can get more expert advise on the "Heating & Cooling" section of the Forum.----Good Luck!!!
 
  #4  
Old 09-11-02, 04:38 PM
A
Master Electrician
Join Date: Dec 2001
Location: Indiana
Posts: 296
Upvotes: 0
Received 0 Upvotes on 0 Posts
Not DIY:

I have to agree with Matt, many things could be wrong, needs serviced, Could spend a lot of money just guessing.
 
  #5  
Old 09-11-02, 04:48 PM
bwetzel
Visiting Guest
Posts: n/a
Make sure you have power at the condenser. There may be a fuse bad at the disconect outside. This would not let the condenser or fan come on, but your furnace fan would still run.
 
  #6  
Old 09-12-02, 01:10 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 646
Upvotes: 0
Received 0 Upvotes on 0 Posts
Re: Central AC fan

Originally posted by GiveMeLight
The fan (outside the house) on my central ac unit doesn't come on when the flip the switch to ON on my thermostat (inside the house). The blower on the furnace blows fairly cool air for a few minutes, then the air warms up again. Whats going on?
GiveMeLight
The fan switch on your thermostat controls whether the air blower motor will run continuously or only when the AC/heat is running. Some people prefer to run their blower constantly to maintain an even temperature in the home. If you look at the switch you are talking about you will probably find that the other position is labeled "auto" meaning automatic with the blower coming on and off with the rest of the unit rather than being "ON" all the time.
--
Tom
 
 