microwave wire
#1
Member
Thread Starter
Join Date: Feb 2002
Location: us
Posts: 71
Upvotes: 0
Received 0 Upvotes
on
0 Posts
microwave wire
I am putting in a new microwave. There is a wire in place that was hooked up to an exhaust fan for my old stove. what I would like to know is if it's ok to use the same wire. The wire is 14/2 bx cable which is on the same circuit with my kitchen light, bedroom light, two hallway lights,and den light. Thank you for your help.
#3

As Sberry mentioned, it depends.
I had a similar scenario; I ended up rewiring the microhood to the other circuit that had lesser load.
Microhood usually draws about 8-9 Amps, depending on make & model. Your 14/2 can handle 15A of total load(well, considering an usual 20% padding, it's actually less than 15A).
With those other loads that you mentioned, that circuit may not be suitable for your new microhood.
I had a similar scenario; I ended up rewiring the microhood to the other circuit that had lesser load.
Microhood usually draws about 8-9 Amps, depending on make & model. Your 14/2 can handle 15A of total load(well, considering an usual 20% padding, it's actually less than 15A).
With those other loads that you mentioned, that circuit may not be suitable for your new microhood.