Conductor sizing for light commercial maintaince building

I asked a question a while back and was told that larger conductors are required for a 200A commercial service than are required for a 200A residential installation. Could someone give me a code reference for this.
Thanks
 
Sponsored Links
  #2  
Old 10-21-02, 02:59 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
NEC Table 310.15 (B)(6) permits a larger ampacity for conductors #4 to 400 MCM (copper) when they are used as Service Conductors for single-phase services for dwellings.
 