I just bought a house and noticed that the electric water heater is wired with 10-2. It is 240 volt with a 30 amp double pull breaker. Black wire to one half of the breaker, white wire to other half of breaker and bare ground to ground bus. The white wire is black taped at each end, is this NEC kosher. Shouldn't 10-3 have been used, same w/ A/C units. Could this be o.k. with my local jurisdiction or just "customary".
 
  #2  
Old 10-27-02, 07:28 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is wired correctly.
 
  #3  
Old 10-27-02, 07:30 PM
Powerjockey2
Visiting Guest
Posts: n/a
I just read John Nelson's description of "pure" 240 circuits and see that electric water heaters and a/c units don't need neutrals. So my situation is probably o.k.
 
  #4  
Old 10-27-02, 08:25 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Yes, it's fine. If you had 10/3, you'd have this problem of having an extra wire with no place to connect it. In fact, I have to commend the electrician who did this. Although reidentifying the white wire is required by code, that step is often skipped.
 
 