grounds
#1
grounds
Can someone point me to some info on the required number of grounds for multiple circuits run in conduit? For instance I am running four circuits in a conduit. How many pairs can share a ground of the same size as the conductors?
Thanks
Thanks
#3
I am talking about grounds not neutrals. I have four circuits going to a junction box which then leave the junction box as romex. Do I need a ground for each circuit or can I run one green wire for all of the circuits which then bonds to the grounds in the romex?
#4
Master Electrician
Join Date: Dec 2001
Location: Indiana
Posts: 296
Upvotes: 0
Received 0 Upvotes
on
0 Posts
one ground, sized to the largest breaker/fuse serving the branch circuits you are installing.
example: 15ampbreaker= 14 ground
20amp breaker= 12 ground
30/40/60amp breaker= 10 ground
example: 15ampbreaker= 14 ground
20amp breaker= 12 ground
30/40/60amp breaker= 10 ground