In the process of remodeling my kitchen, I decided to go with Halo's H99RT (4" remodel). One of the eight holes in the ceiling turns out to be right next to the air conditioning/forced heating duct. The duct material is not metal but flexible plastic (as best as I can describe it). My questions are:
1. Can I install the H99RT housing in this situation?
2. If I can, is there something i need to do to mitigate the effect of generated heat on the duct material?
3. If I cannot, what housing should I use so that I still am able to use the selected trim which is Halo's Eyeball 998?
Any and all suggestions and/or help will be greatly appreciated.
Thanks,
Moe
In the process of remodeling my kitchen, I decided to go with Halo's H99RT (4" remodel). One of the eight holes in the ceiling turns out to be right next to the air conditioning/forced heating duct. The duct material is not metal but flexible plastic (as best as I can describe it). My questions are:
1. Can I install the H99RT housing in this situation?
2. If I can, is there something i need to do to mitigate the effect of generated heat on the duct material?
3. If I cannot, what housing should I use so that I still am able to use the selected trim which is Halo's Eyeball 998?
Any and all suggestions and/or help will be greatly appreciated.
Thanks,
Moe
#2
Member
Join Date: Apr 2002
Location: Canada
Posts: 177
Upvotes: 0
Received 0 Upvotes
on
0 Posts
it appears there is only one optio n when it comes to the 998
for fully protected boxes-H99ICT AIR-TITE IC HOUSING
this is for direct contact with insulation
the only problem is it is not a remodel fixture-it s a new work install
could you possibly replace a 1 foot piece of the plastic with a galvanized heating pipe, would be cheap and relativly easy
unless you are 4 inches away from the pipe i would not suggest the 99rt
to be honest i would cut a larger whole and replace a piece of pipe or change the location
good luck
for fully protected boxes-H99ICT AIR-TITE IC HOUSING
this is for direct contact with insulation
the only problem is it is not a remodel fixture-it s a new work install
could you possibly replace a 1 foot piece of the plastic with a galvanized heating pipe, would be cheap and relativly easy
unless you are 4 inches away from the pipe i would not suggest the 99rt
to be honest i would cut a larger whole and replace a piece of pipe or change the location

good luck
#3
Got answers from Cooper Lighting
Thanks yongeman,
At the same time that I posted the questions here, i had sent the same questions to Cooper Lighting. I received the answers today and here they are for future reference:
1. Yes. Need a 1/2" clearance.
2. No as long as you meet the 1/2" clearance.
3. Would need to use the H99ICT.
Based on this, I am going to go ahead with the install as I do have 1/2" (or can create it).
Again, thanks.
Moe
At the same time that I posted the questions here, i had sent the same questions to Cooper Lighting. I received the answers today and here they are for future reference:
1. Yes. Need a 1/2" clearance.
2. No as long as you meet the 1/2" clearance.
3. Would need to use the H99ICT.
Based on this, I am going to go ahead with the install as I do have 1/2" (or can create it).
Again, thanks.