I'm fairly confident about this question, or at least I was until sombody told me differently today. When you are wiring a 220 volt outlet for misc. shop tools (Air Compressor, Air Conditioner, Saw, and Lathe), do I need to use 12/2 or 12/3 wire and why? Thank you in advance.
J. E. Johns
 
Sponsored Links
  #2  
Old 01-04-03, 02:11 PM
A
Master Electrician
Join Date: Dec 2001
Location: Indiana
Posts: 300
Received 0 Votes on 0 Posts
it depends on what type of load it will be hooked to, if it is going to a welder that
does not use 120volts, then you don't need the white wire, but if you are running it for a
any thing that uses 120volts then you need the white wire 12/3. The reason being in a
120v circuit you need the white wire to take the unused amperage back to the panel, and
not rely on the bare ground to do this. this is all for a safety thing. I could go into detail after detail, but hope this explaines it enough for you.
Thank
Art
 
  #3  
Old 01-04-03, 02:32 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Every place Art used the word "white", I would have used the word "neutral". They're not always the same thing. In almost all cases, you use a white wire -- it's just not always a neutral.

Pure 240-volt tools can use x/2. Without knowing more, it's not possible to say whether or not x=12. The white of the x/2 is used as a hot wire and needs to be reidentified as such with a black marker on each end.

For a particular tool or appliance, you should be able to tell from the instructions whether it needs a neutral (and thus needs x/3), or whether it does not (and thus needs x/2). Most likely, everything you mentioned does not need a neutral.

For your safety, make darn sure you get the value of "x" correct.
 
  #4  
Old 01-04-03, 02:33 PM
A
Aldus0981
Visiting Guest
Posts: n/a
Allow me to clarify that I am using 240 volt circuits.
 
  #5  
Old 01-04-03, 02:37 PM
A
Aldus0981
Visiting Guest
Posts: n/a
Thanks Art and John. At first I thought that Art missunderstood me until John clarified his answer. I understand now and can finish the job and be ready for the inspector Monday morning. Thanks again guys.
J. E. Johns
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: