Wiring 220 volt outlet
I'm fairly confident about this question, or at least I was until sombody told me differently today. When you are wiring a 220 volt outlet for misc. shop tools (Air Compressor, Air Conditioner, Saw, and Lathe), do I need to use 12/2 or 12/3 wire and why? Thank you in advance.
J. E. Johns
J. E. Johns
Master Electrician
it depends on what type of load it will be hooked to, if it is going to a welder that
does not use 120volts, then you don't need the white wire, but if you are running it for a
any thing that uses 120volts then you need the white wire 12/3. The reason being in a
120v circuit you need the white wire to take the unused amperage back to the panel, and
not rely on the bare ground to do this. this is all for a safety thing. I could go into detail after detail, but hope this explaines it enough for you.
Thank
Art
Thank
Art
Every place Art used the word "white", I would have used the word "neutral". They're not always the same thing. In almost all cases, you use a white wire -- it's just not always a neutral.
Pure 240-volt tools can use x/2. Without knowing more, it's not possible to say whether or not x=12. The white of the x/2 is used as a hot wire and needs to be reidentified as such with a black marker on each end.
For a particular tool or appliance, you should be able to tell from the instructions whether it needs a neutral (and thus needs x/3), or whether it does not (and thus needs x/2). Most likely, everything you mentioned does not need a neutral.
For your safety, make darn sure you get the value of "x" correct.