Wiring for a Dryer


  #1  
Old 01-09-03, 10:38 AM
ktlpa
Visiting Guest
Posts: n/a
Question Wiring for a Dryer

I recently purchased an older house and brought with me a 3 wire dryer that plugs into a 30 amp outlet that I have to add. Im going to add a GE Thick Double Pole 30 amp outlet to the main box (Crouse-Hinds) since there is a lot of space let in the box and run the wire to the new outlet. Is an 8-3 wire ok to use or should I be using something else? Is this a safe job? I have changed outlets and brekers before but havent tacklet anything like this. At least the box is close to the dryer so that helps.
Appreciate any advice! Thanks!
 
  #2  
Old 01-09-03, 10:58 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
10/3 is standard wiring for a dryer (but you can use 8/3 if it strikes your fancy). It's a doable (never say "safe") job as long as you know that a panel is still dangerous even with the main breaker off, and you watch where you put your hands, and you torque the screws very tight, and you buy the correct breaker for the panel.

Before you plug it in, convert your 3-wire dryer to a 4-wire dryer (i.e., buy a new 4-wire dryer cord and remove the bonding strap on the dryer).
 
  #3  
Old 01-09-03, 12:00 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
We sometimes should say 10/3 wg,,, I think some people get confused and count the ground wire even though it says on the cable.
 
  #4  
Old 01-09-03, 09:09 PM
Powerjockey2
Visiting Guest
Posts: n/a
Hate to butt in but will anyway

John, I recently purchased a home and the 30 amp 3 prong 220 volt dryer circuit was wired with 10/2 with the black wire and white wire (taped black) to the breakers and the bare ground to the ground bus in the panel. Similar config. as an elec. water heater.

At the plug, the test lite lites up between "L" prong and slant prong1, "L" prong and slant prong2, and between slant prong 1 and 2. Is this kosher? Am I getting 220?
 
  #5  
Old 01-10-03, 06:42 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Powerjockey2, what you have was standard and legal prior to 1996. But ktlpa is installing today, and thus needs to meet today's codes.
 
 