I am wanting to tap (temporaily) a 220 line that currently feeds my well pump. I would like to connect at the toggle switch (220) and run a 110 leg to convert to a new switch/recept. combo outlet. Is this possible since the 2/12 feed to 220 switch has no spare neutral for the 110 receptical. Only two hots and a ground. Can the ground be used as the 110 neutral? (which normally your never supposed to do) But on a 220 2/12 is the ground the neutral but why is that allowed on 220 and not 110.

Thanks
 
  #2  
Old 01-11-03, 10:51 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
The ground could thoeretically be used for the neutral, but not legally, and not without a great compromise to safety. Don't do it!

The 220 needs no neutral. The two hots serve as the return path for each other. If there was a neutral in this cable, there would be no place to connect it at the pump, because the pump has no use for it.
 
  #3  
Old 01-11-03, 11:14 AM
highkamp
Visiting Guest
Posts: n/a
Thanks, I suspected that might be the answer. I will just run a new 110 circuit and leave the 220 alone.
 
 