Wiring a electric water heater
Old 01-19-03, 05:36 AM
cfuller
Does anyone know how I would wire an 80Gallon electric water heater? The book that comes with it just says to read the plate on the water heater for wiring specs. The plate only lists "240/208 volts". Right now I have a 12/2 wire running to it from a 1 pole 20 amp breaker. I am wondering if this is adequate or if I need to increase the connection? i.e should I run a two pole 20 amp breaker. If so how would I make the connections to the tank? It only has a red and black wire coming out of it, no neutral? Any detailed info on amperage, wiring and connections would be appreciated. It doesn't seem like I am getting a full 80 gallons of hot water from the tank.
Old 01-19-03, 06:58 AM
Received 1 Upvote on 1 Post
The normal wiring for water heaters is 10/2 wire and a 30-amp breaker. This is certainly true for 40-gallon and 50-gallon heaters. It is probably still true for 80-gallon heaters too, but you should check the specs. Your water heater will have a lot of stickers on the side. Look for the wattage, a number followed by "W".
A 20-amp 120-volt circuit with 12/2 is nowhere near enough. Neither is a 20-amp 240-volt circuit. There will be no way to make use of the 12/2 wire in any way. A 20-amp 120-volt circuit is providing only one fourth the power that this thing needs, which is why you're getting so little heat.
You may connect the red and black of your heater to the white (marked at each end with a black marker) and black of the new 10/2 you run. Use a double-pole 30-amp breaker. Your water heater needs no neutral. The white is a hot. Although this is probably correct, post back with the specs from the sticker.
Old 01-20-03, 02:31 PM
cfuller
John- The wattage indicated on the sticker is 4500/3380 for total.
There is an upper and lower element and the combined rating is this.
So to wire this I would use a 30A - 2 pole breaker. Then at the tank I connect the black from the 10/2 to the black wire from the tank and the white from the 10/2 to the red from the tank? Disregard neutral connections and just ground the bare copper wire from the 10/2. Easy enough.
Thanks for your help.
Chuck
Old 01-20-03, 04:36 PM
You got it.