Small out bldg. with Air Compressor

I have a small outbuilding set aside from my woodworking shop, inside it I have a 1 hp air compressor. The question is, can I utilize an existing garage wall plug. Can I fabricate a plug and some 12/2 wire and plug it in at the plug receptacle and run the wire in to the small bldg., distance 6 feet, and installing additional wall plug inside the small bldg. The plug in the garage wall is a dedicated plug with only itself on the ciricuit. Or should I pull a separate wire from the panel box to the bldg.? Cost is not an issue, safety is.. thx CM
 
Sponsored Links
  #2  
Old 01-20-03, 06:29 AM
G
Member
Join Date: Dec 2001
Location: Calgary Canada
Posts: 697
Received 0 Votes on 0 Posts
It scares me when someone says fabricate a plug? what exactly do you mean? If cost is not an issue then a new run is better and most likely safer. If you intend to plug something into a receptacle then you must use an approved cord romex is not approved for this and niether is any cable usually run for permenent installations. If this is to be a permenent installation then it is better to do it right in the first place.
 
  #3  
Old 01-20-03, 06:50 AM
clockmaker's Avatar
Member
Thread Starter
Join Date: Nov 2002
Location: usa
Posts: 178
Received 0 Votes on 0 Posts
The fabrification method would be buy a plug ( rated at 15 amps ) and wire 12/2 to it. Pull the wire to the out building, install a metal receptacle box and use a 15 amp plug receptacle. However, I believe I will pull a 10/2 wire to the out bldg. so when I upgrade to a 220 volt compressor the line will be there.
 
  #4  
Old 01-20-03, 07:32 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Bury 12/2 UF cable 18" underground and connect it to a GFCI receptacle in the garage. Protect the cable with conduit where above ground. For only six feet, this is a simple project.

If you want to prepare for future expansion, run 10/3 UF instead and bury it 24" deep. For now, just cap off the red wire at each end.

If you really don't want to go to all this trouble, buy an extra heavy duty (12 gauge or better) outdoor extension cord no longer than what it takes to reach. Put it away after each use.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: