Installing a New Circuit Breaker
#1
Member
Thread Starter
Join Date: Apr 2001
Location: USA
Posts: 69
Upvotes: 0
Received 0 Upvotes
on
0 Posts

I'll be insering a number of QO breakers in my load center. It seems that I will run out of room to connect the white and copper wires. It appears that multiple wires have already been connected to the buss in a single location, but there are some open ones still available.
Some questions:
Can I connect more than one wire to an open space on the bar? Can I connect a second wire to an already used space? Can you mix a white and a copper? etc...
Any rules of thumb would be helpful...
Some questions:
Can I connect more than one wire to an open space on the bar? Can I connect a second wire to an already used space? Can you mix a white and a copper? etc...
Any rules of thumb would be helpful...
#2
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I suggest you install a seperate Grounding terminal bar for terminating the bare Equiptment Grounding conductors. The seperate Grounding bar must be thouroughly bonded to both the metal of the enclosure and the Service Neutral terminal bar.---Good Luck!!!!
#3
You can add a grounding bus bar to your panel to get more connection points for your neutral and grounding wires but make sure it is the appropiate one for your panel. I would also suggest that you seperate the grounding wires to the new bar and leave the neutrals (white wires) on the orginal bar.
and no... only one wire should be on each connection point. Also if someone has done it, make sure there is only one wire on each breaker. I have seen instances where the previous home owner has run new circuits and tied in the new wires to breakers already being used for other circuits trying to keep from replacing the panel.
and no... only one wire should be on each connection point. Also if someone has done it, make sure there is only one wire on each breaker. I have seen instances where the previous home owner has run new circuits and tied in the new wires to breakers already being used for other circuits trying to keep from replacing the panel.