I have three 120v outlets without power. I checked the circuit breaker (20 amps) but it was still in the on position. I removed it from the panel , checked for continuity in the on position & I got it. None in the off position. So the switch should be good.Then volt probed checked the hot wire to neutral & got no reading. All the other breakers read 117v when I did the same thing ( just to make sure I was doing it right). Does this mean I'm grounded somewhere ? I checked the three receptacles that were without power for burn marks or loose connections but they all seem to be good. What can I do next ??????
#2
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes
on
0 Posts