I'm wiring my house and don't have a oven yet, but most likely will have an average freestanding range.. A book at lowes says I can use 10/3 wire? If I don't get one with a elec. cleaning mode. I hoping this would be correct. Because that's what I just ran..I looked at the ovens for power useage and don't understand, (11.5kw 3wire and 3kw) any input on this? Buckman
#2
10/3 can be protected with a 30 amp breaker and is appropriate for a clothes dryer. Most ranges are wired with 8/3 or even 6/3 and are protected by 40 and 50 amp breakers.
11.5kw = 11,500 watts = 47.91 amps @ 240 volts.
Sounds like you need a 6/3 cable with a 50 amp breaker.
11.5kw = 11,500 watts = 47.91 amps @ 240 volts.
Sounds like you need a 6/3 cable with a 50 amp breaker.
#4
Member
Thread Starter
Join Date: Feb 2003
Location: ga
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If I buy enough 6/3 for my oven, can I also use it for my heat pump? since I was told that is what I need there. Or should I buy 6/2, because I'll have an extra not used wire in 6/3? thanks Buckman