Subpanel instal questions


  #1  
Old 04-23-03, 11:01 AM
DWJ
Visiting Guest
Posts: n/a
Subpanel instal questions

I upgrading the electrical in my parents home and need to replace the old fuse boxes with a subpanel. The house was remodeled in the 60's and a 200amp service installed. The old service bacame a subpanel with an assortment of small fuse boxes hanging off it. I am replacing that mess with a new subpanel.

My questions concern wiring between the main panel and new sub. Currently there are three wires feeding the subpanel (2 hot, 1 neutral).

Question #1: Do I need to add a ground wire to link the ground buses on the main and subpanels? If so is that the only grounding point for the subpanel?

I know that the neutral and ground busses cannot be linked in the subpanel.

Question #2: Is it permissible to have a splice in the circuit feeding the stove or other major appliance? I would like to run new wire from the subpanel to the old subpanel and use it as a splice box.
 
  #2  
Old 04-23-03, 11:22 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
First a caution: It is almost certainly not legal for you to do wiring work in your parents' home.

Second, I am going to assume that the main panel and subpanel are in the same building. It sounds like they are.

1. Yes, and yes.
2. Yes.
 
  #3  
Old 04-23-03, 11:48 AM
DWJ
Visiting Guest
Posts: n/a
Thanks for the response.
I am an owner of the house so doing my own wiring should be fine. I also obtained a permit for the work since I want to have it inspected and on record when the house is sold.

Follow-up question.

What size ground wire do I need to use? The subpanel is about 35 feet from the main. I assume the ground wire can be bare.
 
  #4  
Old 04-23-03, 02:47 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
What size are the other wires to the subpanel?
 
  #5  
Old 04-23-03, 04:20 PM
DWJ
Visiting Guest
Posts: n/a
I plan replacing the exisitng wire and using #4 wire. I assume the ground has to be the same size as the others.

I have 1" flexible metal conduit in place to the old sub-panel. Just need to pull out the old wires, shorten the conduit and it attach it to the new subpanel.

Is 1" FMC too small for 3-#4 wires plus ground?

Thanks for your assistance.

David
 
  #6  
Old 04-23-03, 08:19 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
#8 copper ground is big enough. If the size of the breaker protecting the feeder is no larger than 60 amps, you could even use #10.
 
  #7  
Old 04-23-03, 09:02 PM
texsparky
Visiting Guest
Posts: n/a
Post conduit fill for FMC

From 2002 NEC ANNEX C Table C3

For 1" FMC----Type THHN, THWN, or THWN-2 # 4 = 4 conductors

Ampacity from Table 310.16 (75deg.C column) #4 copper = 85 amps. Ground wire could be #10 copper for a 60 amp feeder or # 8 copper up to a 100 amp feeder.
 
 