mobile home

My friends are planning on parking their new big rig in my driveway for the summer. I wanted to give them a 50 amp, 220 plug near the driveway to supply their power needs. I have a 200amp service, square D box with plenty of room but here are my questions.

Do I have enough availible power to supply them? I have 30 amp breakers for the hot water, stove and a heater also all the other generic 15 and 20 amp household circuits. (it's only a 1000 sq foot house) Since this is a short term situation I wasn't particulaly worried about demand and I don't think I would be having everything in the house and the RV on at the same time.

I was planning on loading in a 50 amp breaker with 6 gauge wire. It is about a 90 foot run from the box to the planned outlet. I plan on a 4 wire run, double pole hot, neutral and ground. Armored in the areas where it will be running across the bare basement walls.

Am I missing anything?
 
  #2  
Old 04-24-03, 06:36 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Given what you have said, it seems that you will indeed have enough power to supply them. 200 amp service in a 1000 square foot house without air conditioning or a pool is a very rare set of electrical riches.

I assume that you have verified that their motor home does indeed have a 50-amp 240-volt cord and plug on it. Make sure your receptacle matches their plug. Make sure you provide adequate physical protection for the cable.
 
  #3  
Old 05-04-03, 09:11 PM
P
Member
Thread Starter
Join Date: Feb 2001
Location: Seattle, WA
Posts: 640
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have a weather proof steel box for mounting it on the outside of the house next to the driveway. Since this is an exterior installation, does it need GFCI protection? I looked around the big orange store and I couldn't find GFCI for anything bigger than a 15 amp circut.
 
  #4  
Old 05-04-03, 09:28 PM
green jacket's Avatar
Member
Join Date: Sep 2000
Location: Williamsport and Blue Bell, Pennsylvania
Posts: 489
Upvotes: 0
Received 0 Upvotes on 0 Posts
The big Orange store should stock a Square D 50A 2pole GFCI breaker. The GFCI circuit breaker is the only practical way to achieve GFCI protection a 50amp circuit. Independant GFCI units are available in 240v 2 pole form, however I beleive they normally max out at 30A. Less connections = less problems and work!!!

gj
Sounds like your on track.
What kind of cable are you going to use?
I would recommend using all [SIZE=3]conduit. [/SIZE]
 
 