Mapping electrical system

I'm in the process of mapping the electrical system in the house my wife and I recenlty purchased. I'm not having any trouble with the basics of mapping it out, and calculating wattage on each circuit. What I am wondering is: If there are recepticles on a circuit that don't normally have anything plugged into them ( used mainly for temporary items, such as a vaccuum), is there a standard rule of thumb regarding the number of watts that should be "allocated" to these recepticles when calculating the load on the circuit (to determine how many recepticles should be allowed on one circuit)?
 
Sponsored Links
  #2  
Old 05-07-03, 10:42 AM
texsparky
Visiting Guest
Posts: n/a
Post

Not in residential. In commercial, it is 180 watts per outlet. Residential is basically calculated at 3 watts per sq.ft for the General lighting and receptacle loads.

ie. 1500 sq. ft x 3 watts per sq.ft. =4500 watts

4500 divided by 120 volts = 37.5 amps = (2) 20 amp circuits or (3) 15 amp circuits
 
  #3  
Old 05-07-03, 10:57 AM
C
Member
Thread Starter
Join Date: Apr 2003
Location: USA
Posts: 122
Received 0 Votes on 0 Posts
Thanks, that helps a lot!

Next question (because I don't think there's really a code regulation on this, but I could be wrong): From the Sherlock Holmes work I've done, so far, I know that the dining room light, three bedroom lights, an outside porch light, and a bathroom light are all run on one circuit. I'm going to pull new wire to the bathroom to install outlets (the bathroom has ZERO outlets at this point!), so it'll be on it's own circuit. I had planned on also tieing the bathroom light into this circuit, as well.
(Running from panel to light, to GCFI outlet, to second outlet)

From a practical standpoint, does it make sense to leave all of the bedroom, dining room, and porch lights on this same circuit, or should I split this (I'm going to be re-wiring, anyway, because the old non-grounded wire is in pretty bad shape) into a couple of circuits (or is this simply dependant on the calculation of watts/amps on the line, discussed in the previous posts)?
 
  #4  
Old 05-07-03, 01:59 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
How do you cool your house? Central AC or window AC units?
 
  #5  
Old 05-07-03, 02:00 PM
C
Member
Thread Starter
Join Date: Apr 2003
Location: USA
Posts: 122
Received 0 Votes on 0 Posts
Central AC, why?
 
  #6  
Old 05-07-03, 08:36 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Lighting is a relatively small load. You can put a lot of it on one circuit without problems.

180-watts per duplex receptacle is still a good rule of thumb in residential. In commercial, it's mandatory to use this number, but in residential it is still a good rough planning number.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: