Grounding rod depth?
Old 05-28-03, 08:48 PM
msr
I live in Austin Texas. I am hitting rock at 6". How the heck am I supposed to sink this thing 8'?
Old 05-29-03, 03:03 AM
lestrician
Put it in at an angle.
Old 05-29-03, 04:28 AM
bungalow jeff
You can lay copper rods along the top of rock, but with only 6" cover, you may need a different solution. Is there rebar in the foundation? If so, chip out to expose a bar, ground to that and patch.
Old 05-30-03, 07:10 AM
fewalt's Avatar
Are you sure you are not hitting the footer next to the house??
At times, I've had to come out from the house as much as 14 to eighteen inches to get away from the footer.
fred
Old 05-30-03, 09:44 AM
Received 2 Upvotes on 2 Posts
You may drive a ground rod at a maximum of 45 degrees from vertical. Alternately, you may use a grounding plate. This plate shall expose no less than 2 square feet of surface to exposed soil (12" x 12" = 1 square foot per side = 2 square feet.) Plates of ferrous metal (iron, steel) must be 1/4" thick. Plates of non-ferrous metal (copper, stainless steel) must be .06" thick. Plate must be buried at a minimum of 30" below finished grade. Reference: NEC 250.52(A)(6). Hope that helps.
Juice
Old 05-30-03, 09:03 PM
In order to use the "ufer" ground method, you have to prove that the rebar is, or is connected to at least 20 linear feet of buried rebar.
250.52(a)(3)
Old 05-30-03, 10:30 PM
bungalow jeff
250.52(a)(3)
Good point. Connecting to a horizontal bar on a wall over 20' long should provide this, but there would be no way to be sure, short of screwing up the foundation.
Many homes, particularly old ones, have no rebar to speak of anyway, so the plates may be the way to go, however something would have to be done to increase the ground cover from 6" to 30". Maybe a short retaining wall. Any takers on a minimum area MSR should increase the ground cover?
Old 05-31-03, 05:17 PM
Received 487 Upvotes on 402 Posts
I would call the AHJ and ask for an interpertation.