Electrical Wiring


  #1  
Old 06-12-03, 11:03 AM
ufg8rluver
Visiting Guest
Posts: n/a
Lightbulb Electrical Wiring

I am selling my home and the realtor told us our outlets were "reverse polarity" so we switched the wires around to accomodate the buyer. Now, it is reading "open ground". Is this good or bad or indifferent?!

Thanks!
 
  #2  
Old 06-12-03, 11:18 AM
Join Date: Feb 2003
Location: Indiana
Posts: 317
Upvotes: 0
Received 0 Upvotes on 0 Posts
If the existing receptacles are grounding type (three-hole) yes they MUST be grounded. Some how I suspect someone replaced the polarized (two-hole) receptacles with grounding type without first checking to see if there was a ground present at the box.+
 
  #3  
Old 06-12-03, 11:29 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,986
Received 500 Upvotes on 410 Posts
If there is no ground present, you can legally install gfci receptacles. You only need one on each circuit. The first one can control the others on the same circuit.
 
  #4  
Old 06-12-03, 03:10 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's possible to have "reverse-polarity" at receptacles even if all Grounding connections are perfectly sound and it's possible to correct this situation at only one point where there might be a Black-to-White "cross-over". Much depends, in correcting your problem, on the age/condition/type of the existing wiring, such as metallic or non-metallic boxes and cables. Perhaps you could provide this info.-----Good Luck!!!!
 
  #5  
Old 06-12-03, 03:50 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
With most simple outlet testers, it is not possible to identify a reverse polarity without a ground present. This causes me a little concern in that you may have broken the ground while correcting the polarity.
 
 