Electrical Outlet
Old 06-19-03, 02:41 PM
Rene
Electrical Outlet
Help. I have an oultlet in the garage that is not working. I replaced the outlet recpticle (sp?) and still not working. I have curcuit breakers but they have not been tripped. Do I need a voltage meter to see if the wires are hot? If they are - what is my next step?
Old 06-19-03, 03:04 PM
Received 1 Upvote on 1 Post
Do you know what a GFCI is? If not, we'll try to help you identify and locate it.
Old 06-19-03, 04:55 PM
Rene
I went to Home Depot and got a GFI Receptacle Tester and put it into the socket. The indicator reads: Fault Open Neutral Neutral gound not connected. What can I do to correct the situation. Thanks for your quick reply.
Old 06-19-03, 05:34 PM
Received 499 Upvotes on 410 Posts
Look around the garage for a gfci receptacle that might be tripped. The receptacle might also be an outside receptacle, in the basement, in a bathroom, near the kitchen sink.
Old 06-19-03, 05:55 PM
Rene
I have a GFCI receptacle located in my bathroom which I tripped and still received the same reading as before: Neutral Open. Anymore suggestions? Thanks for your help.
Old 06-19-03, 07:09 PM
Excellent investigation. If your tester is reading open neutral, then it is definitely not a GFCI or breaker problem. You have exactly what your tester says you have, an open neutral.
Sometimes fixing an open neutral is easy, sometimes not. You need to start by shutting off the breaker. Start with the non-working receptacle. Pull it out of the wall and remake all the connections. Check the wire nuts to see if they are tight. Move backstab connections (wires stuck in the little holes) to the adjacent screws (a book on home wiring can show you how to do this properly). Concentrate on the white wires, because that is where the problem is. Then reinstall the receptacle, turn on the breaker, and test. If you've led a good clean life, then it will work. More likely it won't work first time. Move to the next nearest receptacle or switch on the same circuit. Repeat the same procedure. Keep at it until you've done all the switches and receptacles on the circuit, both working ones and non-working ones. If you do them all and it still doesn't work, then have a qualified person tighten the neutral connections in the panel.