Relocation of AC Units


  #1  
Old 07-02-03, 01:55 PM
Emily Z
Visiting Guest
Posts: n/a
Relocation of AC Units

I am in the process of relocating the exterior AC units of my residence forced air system. The units are 220V and originally wired with 10-2 w ground from the service panel. White conductor taped black for second phase. My past experence with 220V service suggest that 10-3 w ground is the usual wire configuration. White being neutral w ground and black red being the loads. Can you hint at why 10-2 w ground might be an acceptable alternative.
 
  #2  
Old 07-02-03, 02:16 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Your A/C is pure 220 and needs no neutral. Even if you had a third wire, you would have nothing at the A/C to connect it to.
 
 