extending from old elect. box


  #1  
Old 07-17-03, 09:45 AM
jandrewnels
Visiting Guest
Posts: n/a
extending from old elect. box

Sorry, just ONE MORE grounding query. I want to extend a circuit from an old receptacle in a metal box. There two wires, looks like rigid conduit (it has a threaded connector entering the box). I read line voltage between the hot lead and the box. Is this an O.K. ground? I've seen posts saying that older circuits, (BX cable w/out a bonding strip for example), although showing voltage to ground, can't serve as a legitimate grounding conductor). We do want to run electronics (computer) off this circuit extension. If this isn't legitimate, can I run a single green grounding wire to a nearby modern box w/ a ground or does the green wire need to go back to the grounding bus in the service panel?
 
  #2  
Old 07-17-03, 09:57 AM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Conduit is a legitimate ground but if you run a new wire it must go to the panel.
 
  #3  
Old 07-18-03, 09:43 AM
J
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 969
Upvotes: 0
Received 2 Upvotes on 2 Posts
Run the new green to the panel OR you may connect it anywhere on the grounding electrode system conductor. (The ground wire that goes from your panel to your ground rod outdoors.) You may not attach it to plumbing anywhere other than within 5-feet from the point of entrance to the building of your water main, and only if that main is metallic and in continuous contact with the earth for min. 10-feet underground.

Hope that helps.

Juice
 
 