I have a small 8'X 8' shed about 100' from the back of my house. I want to put an outlet near this shed. I will only use this outlet to ocassionally power a radio, or a hedge trimmer. Do I HAVE to install a subpanel out there, or can I simply run a line from an existing outside outlet (GFI protected) on the back of the house?
Like I said, I do not want overkill here, since I plan to use the outlet infrequently and with low loads.
Thanks!
 
  #2  
Old 07-24-03, 05:54 PM
green jacket's Avatar
Member
Join Date: Sep 2000
Location: Williamsport and Blue Bell, Pennsylvania
Posts: 489
Upvotes: 0
Received 0 Upvotes on 0 Posts
You could add onto the existing circuit,
However I would run a dedicated circuit, with 10AWG wire back to the main panel. The distance of the run creates a voltage drop, which can be corrected by larger wire. What else is on the existing circuit? !5 or 20 amp? 14, 12, or 10 AWG?

What type of cable/conduit do you intend to use? Depending on the type, it will need to be buried 12 or 18 inches. GFCI protection provided before going underground can reduce the requirement. Conduit (PVC) would be highly recomended. Use THHN wire inside the conduit, or equiv. No romex or UF permitted in the conduit.
What other questions do you have?

gj
 
  #3  
Old 07-24-03, 06:38 PM
Andrew's Avatar
Member
Thread Starter
Join Date: Apr 2003
Location: USA
Posts: 952
Received 14 Upvotes on 10 Posts
Thanks for the quick reply.
There is nothing else on this circuit, and it is wired with 12 gauge and the breaker is 20 amp. The yard is full of underground rocks, boulders, tree roots, etc...so I was planning to run UF cable instead of pipe, due to the anticipated "zig-zaggy" route. I guess my original question was basically whether I could tap off the existing outside outlet, or if I had to run another seperate circuit, since my 100 amp GE breaker box has no empty spaces left, and I don't know of any tandem breakers to fit this panel.
Thanks!!
 
  #4  
Old 07-24-03, 07:05 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sure, you can feed off the existing, no reason not to in this case. I am usually fussy about distance and V drop as Green Jacket is but here I think its irrelevent.
 
  #5  
Old 07-24-03, 07:21 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
If the cable is GFCI-protected before it enters the ground, you only need to bury the cable 12". If you promise never to run more than a hedge trimmer out there, I'll let you use 12/2 UF-B. Sleeve the UF-B in schedule 80 PVC conduit until it reaches the bottom of the trench.
 
 