15 amp outlets and switches on 20 amp circuit

I have just wired my first house and passed my rough inspection.
My question now is do I need to use 20 amp outlets and switches on my 20 amp circuits or can I use less expesive and easy to obtain 15 amp outlets and switches? Thank you in advance for your replys.
 

Last edited by crosvine; 07-25-03 at 10:10 PM.
  #2  
Old 07-26-03, 04:12 AM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,287
Upvotes: 0
Received 0 Upvotes on 0 Posts
As long as there is more than one single receptacle (a duplex receptacle will do), you may use 15A devices for all.
 
  #3  
Old 07-26-03, 06:15 AM
hotarc
Visiting Guest
Posts: n/a
What about a 20 amp circuit, where a switch controls more than 15 amps of lighting?
 
  #4  
Old 07-26-03, 08:10 AM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,287
Upvotes: 0
Received 0 Upvotes on 0 Posts
If one switch controlls 15A of lighting, then it would be the only device on that circuit and require a 20A switch. Devices must be installed within their ratings. The code permits 15A devcies on a 20A circuit as long as it is not the sole device (infering that the load is distributed amongst many 15A devices on the 20A circuit)
 
  #5  
Old 07-26-03, 08:38 AM
hotarc
Visiting Guest
Posts: n/a
"If one switch controlls 15A of lighting, then it would be the only device on that circuit and require a 20A switch"


Yeah I should have realized that.
 
  #6  
Old 07-26-03, 08:43 AM
crosvine
Visiting Guest
Posts: n/a
Well I think I understand, 15 amp recepticals on a dedicated 20 amp kitchen circuit would be ok however 20 amp switches would be needed on a dedicated 20 amp lighting circuit that has only one 20 amp device i.e. 20 amp track lighting. Is this correct?
 
 