outdoor Gfi

Does all wiring done on the outside need to be UF (gray) if conduit is not used? I need to put a GFI recp. outside and the wire that is already there is regular romex. Thanks
 
  #2  
Old 08-14-03, 04:28 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
NM cable may not be used in wet locations. Most places outdoors, including all underground conduit, are considered "wet". It is possible that a very protected spot under a porch might be considered "normally dry". It is also possible that some above-ground outdoor conduit would be considered "normally dry".

UF may be used underground. Unless specifically marked as sunlight-resistant, however, it may not be used where exposed to sunlight.

Not all UF cable is necessarily gray.
 
 