Converting Garage
Greetings!
I am in the process of converting my garage to a workshop. Unfortunately, I have only outlet. Actually two, but the one on the ceiling for the opener doesn't really count.
I also have incandescent light.
I have an existing 200amp box with 4 full slots left. It is located in the basement and my garage is attached and I would say my Main is about 20 ft. away from the garage. So the runs would be fairly easy from a subpanel.
I am fairly new to running wiring, but I believe competent.
My needs will be a dedicated circuit for a lightweight table saw
router, sander and some assorted power tools.
I really don't have any plans or the need for a 220 circuit(s).
I am looking for recommendations on size of subpanel I should use?
What type of wire to run from main to sub?
What size breaker for would I use for the main to jumper to the sub?
Would 12/2 romex be sufficient for about 6~8 outlets?
thanks in advance!!
I am in the process of converting my garage to a workshop. Unfortunately, I have only outlet. Actually two, but the one on the ceiling for the opener doesn't really count.

I have an existing 200amp box with 4 full slots left. It is located in the basement and my garage is attached and I would say my Main is about 20 ft. away from the garage. So the runs would be fairly easy from a subpanel.
I am fairly new to running wiring, but I believe competent.
My needs will be a dedicated circuit for a lightweight table saw
router, sander and some assorted power tools.
I really don't have any plans or the need for a 220 circuit(s).
I am looking for recommendations on size of subpanel I should use?
What type of wire to run from main to sub?
What size breaker for would I use for the main to jumper to the sub?
Would 12/2 romex be sufficient for about 6~8 outlets?
thanks in advance!!
#2
I don't think you need a subpanel at all. A couple of 20-amp circuits on two 12/2 cables should provide all you need.
If you really do want the subpanel anyway (perhaps you've always wanted to wire one), then put in 8/3 to a 40-amp double-pole breaker in the main panel. Use a 12-space panel rated for 100 or 125 amps.
Yes, 12/2 is fine for 6-8 outlets.
Be sure to read a few good books on home wiring before you start. There are a million other important details.
If you really do want the subpanel anyway (perhaps you've always wanted to wire one), then put in 8/3 to a 40-amp double-pole breaker in the main panel. Use a 12-space panel rated for 100 or 125 amps.
Yes, 12/2 is fine for 6-8 outlets.
Be sure to read a few good books on home wiring before you start. There are a million other important details.