Temp bare wires


  #1  
Old 09-14-03, 08:40 PM
gallery
Visiting Guest
Posts: n/a
Temp bare wires

I've been told by an architect that loose wires need to be capped for safety, even though the circuits are off at the panel. Is this really necessary? If so, can you cap it (12-2 NM cable) with a wing nut? If so, how?

(This is temporary. The lights won't be completed/connected until later in the project.)
 
  #2  
Old 09-14-03, 08:45 PM
C
Member
Join Date: Nov 2001
Location: Taylors, SC
Posts: 9,261
Upvotes: 0
Received 0 Upvotes on 0 Posts
Just screw a wire nut over the ends of the individual wires.
 
  #3  
Old 09-15-03, 03:55 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,934
Received 491 Upvotes on 403 Posts
If the wire is still connected to a breaker then the capped off end must be in an accessible box. If you disconnect and abandon both ends then you do anything you want with each end.
 
 