2-Pole Breaker


  #1  
Old 09-17-03, 08:53 AM
markmardon
Visiting Guest
Posts: n/a
2-Pole Breaker

I read somewhere that a 2-pole breaker is strictly for combining into a 240V circuit. Is this true? I need two separate 20A 120V circuits and have an empty 20A 2-pole breaker in the panel (the only available slot). Is it legal to wire them separately?

Thanks much!
 
  #2  
Old 09-17-03, 03:17 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Yes, certainly.
 
  #3  
Old 09-17-03, 03:31 PM
hotarc
Visiting Guest
Posts: n/a
You may run two separate 120 volt circuits off a double pole breaker. Just be aware that a fault on one circuit will also open the other circuit.
 
  #4  
Old 09-17-03, 03:43 PM
markmardon
Visiting Guest
Posts: n/a
Right. OK. That makes sense. Thanks much for the help (and all the help you guys have provided during this never-ending bathroom project of mine).
 
 