Wiring a 240 Volt Outlet to a Subpanel


  #1  
Old 09-17-03, 10:57 AM
mmazzuca
Visiting Guest
Posts: n/a
Question Wiring a 240 Volt Outlet to a Subpanel

When wiring a 240 volt 2-pole 3-wire grounded outlet (NEMA 6-20R) to a subpanel does the ground wire attach to the grounded circuit conductor (neutral) bar or the equipment ground bar?
 
  #2  
Old 09-17-03, 11:09 AM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
You need 4 wires to turn that into a sub. A sub by nature is dual voltage and 240 outlets are not wired or do they have the wires to convert them to one.
 
  #3  
Old 09-17-03, 01:17 PM
winkleal
Visiting Guest
Posts: n/a
I think what he is trying to ask is where to land the bare or green wire for a 240V recepatacle in an existing sub-panel.

Tony
 
  #4  
Old 09-17-03, 01:22 PM
T
Member
Join Date: May 2001
Location: Dry Side of Washington State
Posts: 685
Upvotes: 0
Received 0 Upvotes on 0 Posts
Connect the ground wire from the plug to the equipment ground bar in the sub panel.
 
  #5  
Old 09-17-03, 02:12 PM
S
Member
Join Date: Jun 2002
Location: Brethren, Mi
Posts: 1,564
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry,,, read thru it too fast. Also the neighbor was asking if he could turn an old range cable into a sub,,, must have been on the brain yet.
 
  #6  
Old 09-17-03, 02:44 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
For all panels in all locations at all voltages on all circuits, it can never be wrong to attach the equipment grounding conductor to the grounding bar.

Note that you can get into trouble with the term "ground wire" since it may be ambiguous as to what you are referring to. In this case, it seems obvious that you are referring to the equipment grounding conductor, but in other circumstances it might not be clear whether you mean the (1) grounding electrode conductor, (2) the equipment grounding conductor, or the (3) grounded conductor.
 
  #7  
Old 09-18-03, 05:28 AM
mmazzuca
Visiting Guest
Posts: n/a
Thumbs up

Thanks for the info.

Since I'm connecting the circuit to a subpanel with the neutral separated from the ground I wasn't sure... plus I was getting conflicting answers from peolple that should know.

I did some research and now I understand why the equipment ground is separated from the neutral. For a good explanation check out: http://www.ecmweb.com/ar/electric_code_forum_4/

I also learned that 240 volt AC circuits use the opposite hot wires as returns because they run out of phase.

Know I can hook up the table saw and start working on the stuff the wife wants instead of "Fooling around in my shop!"
 
 