Question Main breaker at meter

Hi:

I am having an old 60-amp fusebox at my seasonal camp replaced with a 100-amp breaker panel. For a variety of reasons, the new panel will be on an inside wall of the house, resulting in the main breaker being located in the meter base.

I would like to secure the main breaker from nosy kids, vandals, etc. Any suggestions? I suppose a small lock would work, but then it's would be another step before killing the power in an emergency.

Thoughts?

Tom Z.
 
  #2  
Old 09-27-03, 08:32 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Yes, the tradeoff is exactly as you indicated and the choice is yours. If a fire department responds, they will just use an axe on the cable and won't be particularly bothered by the lock. I would, however, keep it unlocked while the building is occupied -- for your own safety.
 
  #3  
Old 09-27-03, 08:46 AM
TomZ1's Avatar
Member
Thread Starter
Join Date: Sep 2003
Location: New Hampshire
Posts: 155
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks...does the NEC address this issue?

Tom Z.
 
  #4  
Old 09-27-03, 09:05 AM
CSelectric
Visiting Guest
Posts: n/a
Per NEC Art. 230.92 (2002)

"Where the service overcurrent devices are locked or sealed... ...branch circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accesible location, and shall be of lower ampre rating than the service overcurrent device"

You are feeding a panel, likely containing 15 and 20 amp breakers, so you meet the last part of that rule. As long as your 100A panel is located in a readily acesible location, you're install meets code.
 
 