Main breaker at meter
#1

Hi:
I am having an old 60-amp fusebox at my seasonal camp replaced with a 100-amp breaker panel. For a variety of reasons, the new panel will be on an inside wall of the house, resulting in the main breaker being located in the meter base.
I would like to secure the main breaker from nosy kids, vandals, etc. Any suggestions? I suppose a small lock would work, but then it's would be another step before killing the power in an emergency.
Thoughts?
Tom Z.
I am having an old 60-amp fusebox at my seasonal camp replaced with a 100-amp breaker panel. For a variety of reasons, the new panel will be on an inside wall of the house, resulting in the main breaker being located in the meter base.
I would like to secure the main breaker from nosy kids, vandals, etc. Any suggestions? I suppose a small lock would work, but then it's would be another step before killing the power in an emergency.
Thoughts?
Tom Z.
#2
Yes, the tradeoff is exactly as you indicated and the choice is yours. If a fire department responds, they will just use an axe on the cable and won't be particularly bothered by the lock. I would, however, keep it unlocked while the building is occupied -- for your own safety.
#4
Per NEC Art. 230.92 (2002)
"Where the service overcurrent devices are locked or sealed... ...branch circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accesible location, and shall be of lower ampre rating than the service overcurrent device"
You are feeding a panel, likely containing 15 and 20 amp breakers, so you meet the last part of that rule. As long as your 100A panel is located in a readily acesible location, you're install meets code.