Code Q for recep in bathrooms


  #1  
Old 10-15-03, 10:38 AM
masterjoe
Visiting Guest
Posts: n/a
Unhappy Code Q for recep in bathrooms

I need to install a 110V 15A recep RIGHT NEAR the toilet to plug in a bidet. I have a 20A GFCI recep right on the other side of the wall(toilet is sitting in its separate room). What's the code requirement to install a recep right next to a toilet?? Is it considered a wet area??

My initial plan is to tap off that 20A recep and install 20A recep right near the edge of the toilet bowl. Is this legal??

Thanks in advance.
 
  #2  
Old 10-15-03, 11:17 AM
Rlfrazee
Visiting Guest
Posts: n/a
As long as you are gfci protected I see no problem with what you plan to do. However I am no code expert so wait for reply from one of the moderators....RL
 
  #3  
Old 10-15-03, 11:32 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
As long as the new receptacle inherits the GFCI protection of the one you are tapping off of (i.e., it is wired to the load-side terminals), and assuming the bidet's power requirements are modest, this is fine.

It's not a wet area unless the bidet is designed to shoot water on the wall.
 
 