Adding outlet and running wires in crawlspace.....


  #1  
Old 10-20-03, 11:01 AM
HandymanScott
Visiting Guest
Posts: n/a
Code for Electrical Wires in Crawlspace?

All-

I'm going to be putting in an electrical floor outlet in a small room under the stairway (to plug in a wine cabinet). To get power to this new location, I am going to have to connect to an existing outlet, then take the new power lines down into the crawlspace and over to the new floor outlet.

Any suggestions on how to route the wire in the crawlspace? I was thinking that I would need to put it into conduit and either attach it to the floor joists via brackets -- or can I just drill some holes in the joists and feed the romex thru?

Thanks in advance-


HMS
 
  #2  
Old 10-20-03, 11:40 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,894
Received 477 Upvotes on 393 Posts
If romex is allowed then just drill holes or staple to the side if running the same direction as the joist. Some counties (like Chicago) insist on conduit for everything.
 
  #3  
Old 10-20-03, 01:58 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Don't forget to spring the big bucks for a floor rated box and cover.
 
  #4  
Old 10-21-03, 11:13 AM
HandymanScott
Visiting Guest
Posts: n/a
What size romex would be appropriate? (I'll be attaching this to an existing circuit, and only plan on plugging in a small wine refrigerator.

Thanks-

HMS
 
  #5  
Old 10-21-03, 11:54 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
Whatever size wire is on the current circuit, assuming that is correct. 12 guage for a 20 amp breaker, 14 guage for a 15 amp breaker.
 
  #6  
Old 10-28-03, 07:48 PM
HandymanScott
Visiting Guest
Posts: n/a
Well, I've basically completed the project -- except for one problem.... at my floor outlet, I'm only getting 70 VOLTS AC.

Any idea why?

I tested the outlet that I connected to and have 120 volts.

What I did was drill a hole thru the floor in the wall, fish up some 14/2 romex, then put it in conduit in the crawlspace, then cut the hole in the floor where I wanted my outlet, then attached all the wiring. But only 70 V.

Any idea where I went wrong, or what happened?

The outlet I attached to was not the end of the run, but I don't think that should matter, as I am not blowing any fuses....

HMS
 
  #7  
Old 10-28-03, 08:13 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Plug a lamp into your new receptacle. Does it work? If it works, move the lamp over to the receptacle you tapped off of and plug it in there. Is it the same brightness there?

Most of the time when people read 70 volts, they are misusing their multimeter. Might or might not be the case here. Try the experiment I suggested.
 
  #8  
Old 10-28-03, 08:16 PM
HandymanScott
Visiting Guest
Posts: n/a
No, nothing works. I initially tried to plug in my jigsaw, which wouldn't work, and the lamp also does not work....

The actual length of wire is only ~ 15-18 ft, I can't imagine that there would be a voltage drop of this magnitude...

HMS
 
  #9  
Old 10-28-03, 08:24 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
The 70 volts is phantom. You have an open circuit. One of the wires is not properly connected at one of the two ends. If you have an $8 outlet tester, it would tell you whether it is the black or white wire that isn't connectd. Or you can just double-check your work.
 
  #10  
Old 11-11-03, 03:16 PM
HandymanScott
Visiting Guest
Posts: n/a
Well, it turns out you were right on, and the neutral wire was open along the run.

What puzzles me is that I was using the exterior romex 12/2 which had a hard elastomer cover.

Anywho, I reran a new wire and now everything is working perfectly.

The hardest part of the project was:

1) Drilling up thru the floor beam and wall base w/o drilling thru the wood floor on one side of the wall, or the carpet on the other

and

2) Cutting out the area for the gang box in the floor -- had to cut thru the tongue and groove floor (2 1/2") and the subfloor (3/4") (I'm glad my wife was away during that step!!)

Thanks for all the help!

HMS
 
  #11  
Old 11-11-03, 04:19 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Thanks for the report. We always enjoy hearing the end of the story.
 
 