Is there any limit in the # of receptacles allowed in a circuit..

according to usa code...

ty..
 
  #2  
Old 10-30-03, 11:41 AM
brickeyee
Visiting Guest
Posts: n/a
Not in NEC for a residence. Many AHJs limit you to 8 on a 15 A and 10 on a 20 A circuit. This is also the commercial rule where each recep is 180 V-A, then the circuit is derated 20%. It is probably a good idea to follow the commercial rule unless you are very sure of the loads to be served by the receps.
 
 