Can I run 2 circuits on 12/3 wire?
#1
Can I run 2 circuits on 12/3 wire?
I don't have formal training as an electrician but I have done a lot of wiring over the years. I have to run a lighting and outlet circuit to a new area in my basement. A friend suggested I run one strand of 12/3 to service the 2 circuits. I was not aware this could be done?? I thought each hot lead required it's own neutral.
Are there any drawbacks to running 2 circuits on one 12/3 wire?
Are there any drawbacks to running 2 circuits on one 12/3 wire?
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The answer to your question is yes, you can do this.
This is called a multiwire circuit. To make this work with a single neutral, the two hot wires must come from different legs of the circuit. The current on the neutral will be the difference between the current on each leg. If one leg draws one amp and the other legs doesn't draw any current then the one amp will be on the neutral if one leg draws 3 amps then other leg draws 3 amps then there is no current on the neutral.
The advantage of a multiwire circuit is that you only need to run one cable from the panel to the location where the circuit is used. This is often done to the first location, and then separate cables are run from the first junction box.
The danger with a multiwire circuit is that working on one half of the circuit requires both halves to be shut off. For this reason you need to provide a common trip for the breakers.
Multiwire circuits are frowned upon (by some) for residential installations, because homeowners do not understand them very well or are unfamiliar with them, but are common in commercial applications. The distances in residential applications usually do not justify the use of a multiwire circuit.
This is called a multiwire circuit. To make this work with a single neutral, the two hot wires must come from different legs of the circuit. The current on the neutral will be the difference between the current on each leg. If one leg draws one amp and the other legs doesn't draw any current then the one amp will be on the neutral if one leg draws 3 amps then other leg draws 3 amps then there is no current on the neutral.
The advantage of a multiwire circuit is that you only need to run one cable from the panel to the location where the circuit is used. This is often done to the first location, and then separate cables are run from the first junction box.
The danger with a multiwire circuit is that working on one half of the circuit requires both halves to be shut off. For this reason you need to provide a common trip for the breakers.
Multiwire circuits are frowned upon (by some) for residential installations, because homeowners do not understand them very well or are unfamiliar with them, but are common in commercial applications. The distances in residential applications usually do not justify the use of a multiwire circuit.
#3
I am running aprox. 70 feet before the curcuits hit the first junction box and it is a hard run to fish wire. That is why I thought 12/3 was wonderful.
As I understand it, as long as the breakers are stacked on top of one another, one will pull from one bar and one from the other.
As I understand it, as long as the breakers are stacked on top of one another, one will pull from one bar and one from the other.
#4
As long as they are stacked on on top of the other, and as long as they are not those skinny tandem breakers, they will get power from separate legs.
I generally try to discourage multiwire circuits. However, they do have their uses, and you situation may be one of them. But you may find that you can simply fish two 12/2 cables at the same time about as easily as one 12/3.
If you do decide to use the multiwire circuit, I have three suggestions:[list=1][*]Use a voltmeter to ensure that you have 240 volts between the black and red.[*]If you need GFCI or AFCI protection on this circuit, then split the 12/3 to two 12/2s in the first junction box you come to. If you don't understand why I said this, then maybe you don't understand multiwire circuits well enough yet to install one.[*]Use a double-pole breaker, even in situations where it is not technically required.[/list=1]
I generally try to discourage multiwire circuits. However, they do have their uses, and you situation may be one of them. But you may find that you can simply fish two 12/2 cables at the same time about as easily as one 12/3.
If you do decide to use the multiwire circuit, I have three suggestions:[list=1][*]Use a voltmeter to ensure that you have 240 volts between the black and red.[*]If you need GFCI or AFCI protection on this circuit, then split the 12/3 to two 12/2s in the first junction box you come to. If you don't understand why I said this, then maybe you don't understand multiwire circuits well enough yet to install one.[*]Use a double-pole breaker, even in situations where it is not technically required.[/list=1]
#6
A few questions/comments.
"The danger with a multiwire circuit is that working on one half of the circuit requires both halves to be shut off. For this reason you need to provide a common trip for the breakers."
This is not code but a suggestion. Code says only if both circuits terminate on the same device yoke.
"The distances in residential applications usually do not justify the use of a multiwire circuit."
You obviously haven't wired many houses. Multi wires are a good way to lighten the wiring fill in a panel. Also it greatly cuts down the number of homeruns. Try it next time you have a new house with a full 40 circuit panel.
"and as long as they are not those skinny tandem breakers"
The most important thing to remember!
"If you need GFCI or AFCI protection on this circuit, then split the 12/3 to two 12/2s in the first junction box you come to. If you don't understand why I said this, then maybe you don't understand multiwire circuits well enough yet to install one."
I'm a licensed electrician and I still don't get what you mean. The only way to use GFCI/AFCI with a multi-wire is a two pole GFCI/AFCI breaker.
"The danger with a multiwire circuit is that working on one half of the circuit requires both halves to be shut off. For this reason you need to provide a common trip for the breakers."
This is not code but a suggestion. Code says only if both circuits terminate on the same device yoke.
"The distances in residential applications usually do not justify the use of a multiwire circuit."
You obviously haven't wired many houses. Multi wires are a good way to lighten the wiring fill in a panel. Also it greatly cuts down the number of homeruns. Try it next time you have a new house with a full 40 circuit panel.
"and as long as they are not those skinny tandem breakers"
The most important thing to remember!
"If you need GFCI or AFCI protection on this circuit, then split the 12/3 to two 12/2s in the first junction box you come to. If you don't understand why I said this, then maybe you don't understand multiwire circuits well enough yet to install one."
I'm a licensed electrician and I still don't get what you mean. The only way to use GFCI/AFCI with a multi-wire is a two pole GFCI/AFCI breaker.
#7
"If you need GFCI or AFCI protection on this circuit, then split the 12/3 to two 12/2s in the first junction box you come to. If you don't understand why I said this, then maybe you don't understand multiwire circuits well enough yet to install one." I'm a licensed electrician and I still don't get what you mean. The only way to use GFCI/AFCI with a multi-wire is a two pole GFCI/AFCI breaker.
#8
Originally posted by John Nelson
Yes, very true of AFCI, since AFCI receptacles haven't been marketed yet. But GFCI protection can certainly be provided with ordinary GFCI receptacles, providing you do as I said.
Yes, very true of AFCI, since AFCI receptacles haven't been marketed yet. But GFCI protection can certainly be provided with ordinary GFCI receptacles, providing you do as I said.
#9
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My comment regarding multiwire circuits not being justified in houses had to do with adding circuits, not with new construction. I was also thinking more along the lines of do-it-yourselfers, not electricians.
Even so, if I were building a house or having my house completel,y rewired, I would make it clear that I wanted no multiwire circuits.
Even so, if I were building a house or having my house completel,y rewired, I would make it clear that I wanted no multiwire circuits.
#10
Funny how things are foreign to different people. Multi-wire branch circuits are the norm where I come from. We only use seperate neutrals if it is spec'd or if it is for an isolated circuit (clean power).
#13
If it were me, I would run a 14/3 to a 2 gang box with 2 duplex receptacles each on a circuit. Then a power strip off each outlet. With today's home theaters there is no way you'll be able to plug everything into the wall. You'd need 4 or 5 duplexes. I must have 8 or 9 things to plug in at mine.
I also don't understand people's obsession with 12 wire. Any residential circuit (barring kitchen, bath, basement, garage, laundry, any utilitarian circuits) can be run in 14 wire.
If you use this stuff you know what I'm talking about. Pig tails and splices are much easier and neater in 14 and device hook up is also much easier. You just cannot put as many devices or lights on a circuit.
With the advent of AFCI's we put each BR on it's own circuit anyway. Having 4 or 5 receptacles and a light on a circuit is far from full.
I have been told running 12 is safer which is total BS.
Running spares to an attic I can see using 12/3, just in case, but for general use 14 is fine.
I also don't understand people's obsession with 12 wire. Any residential circuit (barring kitchen, bath, basement, garage, laundry, any utilitarian circuits) can be run in 14 wire.
If you use this stuff you know what I'm talking about. Pig tails and splices are much easier and neater in 14 and device hook up is also much easier. You just cannot put as many devices or lights on a circuit.
With the advent of AFCI's we put each BR on it's own circuit anyway. Having 4 or 5 receptacles and a light on a circuit is far from full.
I have been told running 12 is safer which is total BS.
Running spares to an attic I can see using 12/3, just in case, but for general use 14 is fine.
#14
hornetd
--------------------------------------------------------------------------------
Originally posted by mark8076
Another consideration, one of the circuits is for a home theatre system. Could I get interferrence if it is one leg of the 12/3 wire?
Nucleus
I would highly recommend running a separate 12/2 for this purpose.
--------------------------------------------------------------------------------
Dare I ask why?
--------------------------------------------------------------------------------
Originally posted by mark8076
Another consideration, one of the circuits is for a home theatre system. Could I get interferrence if it is one leg of the 12/3 wire?
Nucleus
I would highly recommend running a separate 12/2 for this purpose.
--------------------------------------------------------------------------------
Dare I ask why?
Speedy Petey
If it were me, I would run a 14/3 to a 2 gang box with 2 duplex receptacles each on a circuit. Then a power strip off each outlet. With today's home theaters there is no way you'll be able to plug everything into the wall.
If it were me, I would run a 14/3 to a 2 gang box with 2 duplex receptacles each on a circuit. Then a power strip off each outlet. With today's home theaters there is no way you'll be able to plug everything into the wall.
Last edited by Nucleus; 11-17-03 at 05:21 AM.
#15
Originally posted by Speedy Petey
I also don't understand people's obsession with 12 wire. Any residential circuit (barring kitchen, bath, basement, garage, laundry, any utilitarian circuits) can be run in 14 wire. With the advent of AFCI's we put each BR on it's own circuit anyway. Having 4 or 5 receptacles and a light on a circuit is far from full.
I also don't understand people's obsession with 12 wire. Any residential circuit (barring kitchen, bath, basement, garage, laundry, any utilitarian circuits) can be run in 14 wire. With the advent of AFCI's we put each BR on it's own circuit anyway. Having 4 or 5 receptacles and a light on a circuit is far from full.
#17
True most circuits don't call for any more than a 15 amp max. load these days. But then again, when my first house was built in the 1950s, four 15 amp fuses ran the whole house. Let's see you run a whole house now on four 15 amp circuits. I'm running 20 amp outlet circuits on the chance maybe someday my wife will want to plug in a space heater on a cold day. Or who knows what new electronics they will come up with in 20 years. As long as I'm running the wire I might as well run #12 and hopefully avoid having to fish additional circuits through finished walls in the future.
#18
Originally posted by Nucleus
Nucleus
I would highly recommend running a separate 12/2 for this purpose.
Ground loop
Originally posted by mark8076
Another consideration, one of the circuits is for a home theatre system. Could I get interferrence if it is one leg of the 12/3 wire?
Another consideration, one of the circuits is for a home theatre system. Could I get interferrence if it is one leg of the 12/3 wire?
I would highly recommend running a separate 12/2 for this purpose.
hornetd Wrote:
Dare I ask why?
Dare I ask why?
Ground loop
I have wired a number of radio installations including the studio of a major news radio station. We made every effort to keep all of the equipment in a single audio pathway on a single ground. One of the ways we did that is by the judicious use of multiwire branch circuits because those circuits can carry two or three times the current and only have one grounding conductor in the raceway or cable. IMuHO using multiple cables in place of a multiwire branch circuit is more rather than less likely to cause a ground loop.
--
Tom
Last edited by hornetd; 11-16-03 at 07:11 PM.
#19
Originally posted by hornetd
I have wired a number of radio installations including the studio of a major news radio station. We made every effort to keep all of the equipment in a single audio pathway on a single ground. One of the ways we did that is by the judicious use of multiwire branch circuits because those circuits can carry two or three times the current and only have one grounding conductor in the raceway or cable. IMuHO using multiple cables in place of a multiwire branch circuit is more rather than less likely to cause a ground loop.
--
Tom
I have wired a number of radio installations including the studio of a major news radio station. We made every effort to keep all of the equipment in a single audio pathway on a single ground. One of the ways we did that is by the judicious use of multiwire branch circuits because those circuits can carry two or three times the current and only have one grounding conductor in the raceway or cable. IMuHO using multiple cables in place of a multiwire branch circuit is more rather than less likely to cause a ground loop.
--
Tom
Also, how would you avoid ground loop with a multiwire circuit? The circuits can't be on the same phase unless they are exactly balanced.
Originally posted by hornetd
IMuHO using multiple cables in place of a multiwire branch circuit is more rather than less likely to cause a ground loop.
IMuHO using multiple cables in place of a multiwire branch circuit is more rather than less likely to cause a ground loop.
#20
Originally posted by mark8076
True most circuits don't call for any more than a 15 amp max. load these days. But then again, when my first house was built in the 1950s, four 15 amp fuses ran the whole house. Let's see you run a whole house now on four 15 amp circuits. I'm running 20 amp outlet circuits on the chance maybe someday my wife will want to plug in a space heater on a cold day. Or who knows what new electronics they will come up with in 20 years. As long as I'm running the wire I might as well run #12 and hopefully avoid having to fish additional circuits through finished walls in the future.
True most circuits don't call for any more than a 15 amp max. load these days. But then again, when my first house was built in the 1950s, four 15 amp fuses ran the whole house. Let's see you run a whole house now on four 15 amp circuits. I'm running 20 amp outlet circuits on the chance maybe someday my wife will want to plug in a space heater on a cold day. Or who knows what new electronics they will come up with in 20 years. As long as I'm running the wire I might as well run #12 and hopefully avoid having to fish additional circuits through finished walls in the future.