electrical/ generator connection


  #1  
Old 11-18-03, 03:57 AM
harlowm
Visiting Guest
Posts: n/a
electrical/ generator connection

I want to install a 40 kw generator. If I have an existing 400 amp service, how is the transfer switch connected to the main service.
 
  #2  
Old 11-18-03, 08:46 AM
texsparky
Visiting Guest
Posts: n/a
A 40 kw generator will only provide with a 166 amps at 240 volts. There will need to be some load shedding involved.
Go to This Link provided by Speedy Petey for more information.
 
  #3  
Old 11-18-03, 02:23 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is it a single 400A service or parallel 200A?
With 2- 200A services we sometimes will put all the generator loads in one panel and all the non-critical loads in the other, being careful to try and keep the load as balanced as can be. You can then use a less expensive 200A transfer switch.

With a single 400A service you'll need a 400A transfer switch. Depending on the gen-set you get this can be automatic or manual.

Is this a home or commercial. 40kw is a whopper for a home.
 
 