Solid vs Stranded equivalence

Would an 8 conductor (19 ga) stranded wire be equivalent to an 8 ga solid conductor wire?
 
Sponsored Links
  #2  
Old 12-10-03, 12:35 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
8-gauge is 8-gauge, whether stranded or solid. But 8-conductor is not equivalent to 8-gauge. Exactly what are you asking?
 
  #3  
Old 12-10-03, 12:47 PM
Member
Join Date: Dec 2001
Location: Calgary Canada
Posts: 697
Received 0 Votes on 0 Posts
you might want to check out this site.
http://www.epelectric.com/apogee/foe_html/fbwss.htm

There are benifits and drawbacks to both stranded and solid wire could you be a little more specific on what your needs are?
 
  #4  
Old 12-11-03, 06:20 AM
Dave_D1945's Avatar
Member
Thread Starter
Join Date: Dec 2003
Location: Bay Area, CA
Posts: 1,178
Received 0 Votes on 0 Posts
A friend is helping build a shop and they want to use #8 wire to connect the electrical feed. He was asking me if an 8 conductor 19 ga stranded wire was equivalent to an 8 ga solid conductor wire.
 
  #5  
Old 12-11-03, 07:03 AM
Member
Join Date: Dec 2001
Location: Calgary Canada
Posts: 697
Received 0 Votes on 0 Posts
No they are two different things. 8 ga solid and 8 ga stranded are equivilent but 19 ga is only equivilent to 19 ga wire. I think it would be wise for your friend to do some reading before attemping to do anything electrical, he might be missing some important information or at least be missunderstanding so basic concepts the he should really get a grip on before undertaking a project such as this. There are many good books on the market and it is my feelings that they are essential to DYI'ers safety.
 
  #6  
Old 12-11-03, 09:52 AM
brickeyee
Visiting Guest
Posts: n/a
You really need a wiring handbook. A #8 wire is 0.12849 inches in diameter. A #19 wire is 0.035890 inches in diameter. The #8 will be stranded and made up of 7 smaller gauge wires that add up to at least the same cross section as a #8 solid wire (stranded usually has a slightly larger cross section than the nominal solid).
This is not a good place to learn from a mistake.
 
  #7  
Old 12-11-03, 10:55 AM
Dave_D1945's Avatar
Member
Thread Starter
Join Date: Dec 2003
Location: Bay Area, CA
Posts: 1,178
Received 0 Votes on 0 Posts
This isn't a diy project. We were splitting firewood on a Saturday morning and he asked me. I wasn't sure so I thought I'd ask. I'll tell him to ask the electrician doing the job.
 
  #8  
Old 12-11-03, 11:22 AM
mattgg
Visiting Guest
Posts: n/a
He must mean, "Is a stranded conductor made of eight 19 ga wires equivalent to one 8 ga solid wire?" Based on the diameters given by brickeyee, it appears that the answer may be "yes". Why anyone would ask the question that way, I don't know. You don't generally make your own stranded conductors. I'd bet the friend misunderstood what the electrician was saying.
 
  #9  
Old 12-11-03, 12:38 PM
brickeyee
Visiting Guest
Posts: n/a
Maybe close, but not close enough. The cross section area is what determines ampacity, and #8 is 16,509 circular mils, and 8 strands of #19 are only 10, 305 circular mils. A #10 wire is 10,383 circular mils. So instead of about a 40 amp capacity, you are just under 30 amps.
Here is a decent wire table:
http://mech296.engr.scu.edu/referenc...GAUGETABLE.htm
 
  #10  
Old 12-11-03, 03:09 PM
Dave_D1945's Avatar
Member
Thread Starter
Join Date: Dec 2003
Location: Bay Area, CA
Posts: 1,178
Received 0 Votes on 0 Posts
brickeyee-

That's what I was looking for - current capacity in stranded vs solid wire. Let's call the poor phrasing of the original question a senior moment, ok?
 
  #11  
Old 12-12-03, 11:39 AM
brickeyee
Visiting Guest
Posts: n/a
You have to use the wire at whatever gauge the manufacturer marked on it for house wiring. Internal equipment wiring is a different matter. You are not likely to find a piece of #10 wire in an electric stove. None of the heating elements individually need that much ampacity, and higher temperature insulation is typically used allowing a smaller wire size.
Since wire is normally only available in the discrete sizes, a stranded wire is made up by finding the cross section of the solid wire, dividing by the number of strands, and finding the smallest solid wire that is larger than the required strand cross section. The error is less with higher stranding counts.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: