Dishwasher receptacle - GFCI req'd?
Old 12-16-03, 11:30 AM
P
Is the dishwasher receptacle (15A dedicated circuit; located under the sink) required to be GFCI protected?
Old 12-16-03, 11:58 AM
R
No.
Old 12-17-03, 10:27 AM
charlie b
I concur. The reference is NEC article 210.8, "Ground-Fault Circuit-Interrupter Protection for Personnel."
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.
(6) Kitchens - where the receptacles are installed to serve the countertop surfaces.
Old 12-17-03, 05:56 PM
rob1kva
I agree with racraft the dishwasher is an appliance whice is secured into the counter if is cord & plug connected {like the one Iremoved this week it does not need GFCI protection. The receptecle for the fridge also does not require protection.
Old 12-18-03, 08:26 AM
P
Thanks for the replies and the references.