What makes best ground?


  #1  
Old 12-22-03, 01:20 PM
zeringue
Visiting Guest
Posts: n/a
What makes best ground?

Is 8' depth of copper ground rod good enough, or should two 8' be connected and driven to 16'? I'm doing some re-wiring and just wondering if what's here is good enough for residential dwelling. If there are any "standards" specs on this, please let me know where to look. Thanks!
 
  #2  
Old 12-22-03, 04:19 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,029
Received 513 Upvotes on 418 Posts
Two 8' rods 10' apart is normal. You don't connect them together into a 16' rod.
 
  #3  
Old 12-22-03, 05:01 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
You need a second ground as well. This can be the water pipe, if it is metal and if it extends outside the house and into the ground for at least ten feet. Whether the water pipe is used as a ground or not, the interior water pipes must be connected to your ground system if they are metal.
 
  #4  
Old 12-22-03, 05:34 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
NEC 250.50 through 250.70 is all about grounding electrodes and conductors. If you wish to look it up.

Basically if you have a metal water pipe feeding your house, and it extends at least 10' from the house, it must be used as an electrode. You must also jump out the meter and any other equipment that breaks or can break the pipe integrity, ie: unions.
If you use the water pipe as an electrode you MUST supplement that with a rod electrode.

If no metal water pipe is present only ONE (or more) electrode(rod) is required by the NEC. Local codes vary greatly as do the grounding electrode conductor sizing. The catch is the rod must have a resistance of 25 ohms or less. If not it must be supplemented by another electrode, at least 6' apart. I will say, in all my years I have never seen an inspector ohm out a ground rod. It's more of a judgement call by the installer.

As racraft said. In any case the metal piping in the house must be bonded.
 
 